Anonymous Poster

33 KV system

11/12/2009 1:54 AM

we have built a factory with 33 kv system as the HT supply. there is a 33 kv/415 V transformer along with 33 kv siemens switchgears.

If the electricity board gives us 11 KV supply instead of 33 KV supply, Can this existing system be run on 11 KV system??

The actual story is, our load demand is 1400 KVA, for which 11 KV is sufficient. But the load is expected to double in one year, for which 33 kv is required (as per electricity board).

If we take 33 KV, at present to meet the existing 1400 kva load, we need to pay idle charges for the power not being used.

Please clarify

Regards,

PG

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: 33 KV system

11/12/2009 3:06 AM

You have to change the Transformer and the switchgears. May not be worth it.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: 33 KV system

11/12/2009 8:01 AM

If you are sure of future expansion in load, you can retain the 33kV Switchgear already procured & installed and extend 11kV supply to the same for the time being. Nothing will happen.

But, the same cannot be told of the transformer. If you have a 33kV/415V Transformer and extend only 11kV to it, the LV side voltage will only be 1/3rd of 415V. So, you MUST replace the transformer with a 11kV/415V one.

Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#3

Re: 33 KV system

11/12/2009 11:59 PM

Buy a 33/11/415 Volts transformer.So u can change over easily.This is a standard method we have used in Many places.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Anonymous Poster
#4

Re: 33 KV system

11/13/2009 12:04 AM

You will have to change your transformer(s) and may have a problem on capacity. 33kv system tranlates to a small amperage capability; so for lower voltage, the amperage goes up for the same total KVA. Your switchgear may not take it; the higher amperage, and perhaps your controls and protection schemes change alot. Long story, short ending, take service at 33 KV, the cost of conversion would be excessive and a waste of money considering your statement of load increases may eventually require 33 kv service anyway.