Anonymous Poster

ELCB tripping

11/12/2009 6:35 AM

At site there is a electric supply board for single phase(230 V- india) supply. The power source is a DG set (14 A, 415 V, 50 Hz, three phase). DG is earthed (both body and neutral). supply board body is also earthed. There is an MCB with 30 mA ELCB. But even when we touch the neutral to the earth, the ELCB is not tripping. why?? OUr purpose is to ensure the proper operation of the ELCB. what other test can be carried out??

Regards,

PG

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: ELCB tripping

11/12/2009 6:40 AM

<...touch the neutral to the earth, the ELCB is not tripping. why?...>

Because the imbalance of current between live and neural is <30mA at the moment the test is carried out.

Most ELCBs have a test button. Simply press it!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#2
In reply to #1

Re: ELCB tripping

11/12/2009 6:47 AM

You are right. Manually the ELCB is tripping. If by chance, if there is any damage to skin of insulation, the leakage current may harm the personnel using the electrical equipment. We want to checkt the electrical tripping of the ELCB

REgards

PG

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: ELCB tripping

11/12/2009 7:43 AM

Please note that even what you call "Manual Tripping" is, in fact, only electrical tripping as far as the ELCB is concerned. Because, when you press the TEST Button, you are actually simulating the earth leakage conditions 'electrically'.

If your intention is to "TEST" the functioning of the ELCB by actually subjecting a person to electrocution, I doubt if anybody would be ready to undergo such a test.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: ELCB tripping

11/12/2009 7:43 AM

The manual button does this by introducing an unbalanced load within the equipment.

To check outside the equipment, simply connect a load >30mA to the live conductor downstream of the ELCB, and to the neutral conductor upstream of it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#5

Re: ELCB tripping

11/12/2009 8:54 AM

DG is earthed - both neutral and body.

Then why the touching of neutral to earth will pass the current (both at equipotential?) unless the cable length is long enough to have some resistive drop, enough to carry the 30ma current.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: ELCB tripping

11/12/2009 10:13 AM

There has to be a current imbalance on the live and neutral feeding the load, both conductors passing through the ELCB, for the ELCB to operate.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#8
In reply to #6

Re: ELCB tripping

11/12/2009 12:54 PM

ELCB or RCD?

Reply
Anonymous Poster
#7

Re: ELCB tripping

11/12/2009 10:32 AM
Reply