Substation Generators Tripped -- Why?

11/12/2009 2:08 PM

We have in our substation 5 sources
3 generators each of them 6 mw , 6.6kv
2 feeders from national grid 10mw 6.6kv

our grounding system by using ground transformer zig-zag transformer with grounding resistance connected from it's star point to earth.

we have also capacitor banks for power factor correction .

all of these connected to main bus par by oil circuit breaker.
The load is 12mw where each source loaded 3mw with one feeder from national grid is standby.
Once a day the operator notice that the feeder which loaded was only two phases loaded with normal current while the third phase was loaded with very low current , so he opened the circuit breaker of that feeder , when he did that , all generators tripped except one generator stay loaded for a few seconds because of it's opening circuit failure , also both the ground transformer and the resistance were burned

it is working since 1970 so it is old ,

i hope it is clear for you

can i discuss this with you?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Jun 2009
Location: Sri Lanka
Posts: 16
#1

Re: Substation Generators Tripped -- Why?

11/13/2009 6:27 AM

Can you explain the same with a drawing. I cant catch it but am interested.

Register to Reply
Commentator

Join Date: Nov 2009
Location: PA
Posts: 83
Good Answers: 1
#2

Re: Substation Generators Tripped -- Why?

11/13/2009 1:44 PM

May be it couldnt take the load. Is the load shared by 3 generators (3+3+3) and 1 feeder (3) ? if so the loss of feeder will overload the generator, since the 2 generators opened, the excess unbalanced zerosequence current (because u said only 2 phases had good current ) caused the ground transformer to burn.

Register to Reply
Member

Join Date: Oct 2009
Posts: 5
#3
In reply to #2

Re: Substation Generators Tripped -- Why?

11/14/2009 10:19 AM

yes the load shared by 3 generators and one feeder,

why when the operator switched off the faulty feeder , other generators tripprd and ground transformer burn?

the ground transformer burn due to flow of zero sequnce current , how the path for this current ?

Register to Reply