We have in our substation 5 sources
3 generators each of them 6 mw , 6.6kv
2 feeders from national grid 10mw 6.6kv
our grounding system by using ground transformer zig-zag transformer
with grounding resistance connected from it's star point to earth.
we have also capacitor banks for power factor correction .
all of these connected to main bus par by oil circuit breaker.
The load is 12mw where each source loaded 3mw with one feeder from national grid is standby.
Once a day the operator notice that the feeder which loaded was only
two phases loaded with normal current while the third phase was loaded
with very low current , so he opened the circuit breaker of that
feeder , when he did that , all generators tripped except one generator
stay loaded for a few seconds because of it's opening circuit failure ,
also both the ground transformer and the resistance were burned
it is working since 1970 so it is old ,
i hope it is clear for you
can i discuss this with you?