Motor Operated Valve (MOV)

11/12/2009 1:11 PM

Here's a strange case. One of our MOVs didn't open on remote command & it even didn't open on local command too.Then the operator had to open it manually by hand.After that the MOV was opening in remote local command.It's again confirmed the next day also.But actually what happened?.Has it anything to do with the pressure ?The valve was a globe valve..pls help me .

__________________
"Know something about everything and everything about something"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jan 2009
Posts: 227
Good Answers: 11
#1

Re: Motor Operated Valve (MOV)

11/12/2009 2:53 PM

Something (bacterial buildup or lime precipitation in the line?) may have been stuck to the ball, or there may have been dirt or a mechanical obstruction on the actuator. The actuator drive was not strong enough to overcome it, but the operator was.

Another possibility is lubrication breakdown in the actuator mechanism. Manually forcing it redistributed the lubricant so it will work for a while. You can check for this by comparing actuator current or manual operating force with other similar units.

The next step is to determine the most probable cause and take steps to prevent a recurrence.

Register to Reply
Participant

Join Date: Nov 2009
Posts: 3
#2

Re: Motor Operated Valve (MOV)

11/12/2009 4:52 PM

check the control circuit , limit switch, or contactor contacts

make some maintenance and overhaul to see the conditions may be something stuck there

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Motor Operated Valve (MOV)

11/12/2009 6:36 PM

Yes, my first suspect would be the limit switches. If they do not indicate the position of the valve correctly, the Motor Operator will not respond to a command. it is intended as a fail safe against accidentally giving the MOV an Open and Close command at the same time, or to prevent over travel. But if the switches fail or the contacts corrode, the "fail safe" mode is to do disable the motor operation.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Commentator

Join Date: Jun 2009
Location: Between India & Australia
Posts: 71
Good Answers: 3
#4

Re: Motor Operated Valve (MOV)

11/12/2009 11:34 PM

Is this valve placed in oil service, if so the reason may be oil degradation leading to sludge formation across valve and other such surfaces. You need to get your oil checked for oxidation and possibly get it electrostatically cleaned.

__________________
Continuous Learning
Register to Reply
Guru
Spain - Member - New Member Engineering Fields - Nuclear Engineering - New Member

Join Date: Oct 2007
Location: Madrid, Spain
Posts: 716
Good Answers: 25
#5

Re: Motor Operated Valve (MOV)

11/13/2009 2:17 AM

Has somebody look at the limit and torque switches status when electrical command doesn't go?

The opening and closing are done always in the same system conditions? If MOV actuator is not properly adjusted, it can operate under no load condition (no delta P) and fail if delta P is present.

The globe valve is balanced type? What's the flow direction?

I find difficult for a globe valve to get stuck everyday by any deposit type.

What type of fluid can build in just one day a deposit which stucks the disc into the seat in such a way as to block a motor operator?

A simple way to see if it's a problem with pressure or just switches misadjustment is to measure the motor current while trying to remote or local actuating the valve. If the current is high (locked rotor) then is a valve problem (pressure). If no current is present then there is a problem with switches adjustment.

By the way, which motor operator trademark is?

Kind regards

__________________
It's stupid to discuss about AI: We´ve reached by the "B" way. We' ve producing men as clever as machines.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Motor Operated Valve (MOV)

11/13/2009 3:04 AM

An MOV not far from here displayed a similar phenomenon. The cause was eventually traced to the magnetism from the steel non-return valve nearby being sufficiently strong to operate the reed switch that prevented the device from motoring.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#7
In reply to #6

Re: Motor Operated Valve (MOV)

11/13/2009 3:43 AM

First impressions on reading could be the limit switches set up incorrectly or even control wire connections not connected tightly therefore intermittent fault also broken wire, may arise again if this not checked, but if now operating would suspect that unit had seized & the operation of MOV freed off,would still check out control cct to make sure!

Register to Reply
Power-User

Join Date: Mar 2009
Location: O'er looking the silvery Tay
Posts: 255
Good Answers: 18
#8

Re: Motor Operated Valve (MOV)

11/13/2009 4:52 AM

Dear Giri,

I too would vote for the limit switch scenario as being 'top of the list' of possibles.

Remember that to start the valve opening it is the opposite end of travel switch which is suspect as this is the device which prevented the actuator going 'over limit' when it last ran open properly,(as against the one it will be currently at). Depending on the environment a bit of stiction can easily cause this problem and usually a squirt of WD-40 or similar works wonders.

If you have a population of these valve actuators it would be as well to service them all whist dealing with this issue.

Good luck,

Massey.

__________________
If it ain't broke,leave it well alone .........until it comes looking for you!
Register to Reply
Guru
Hobbies - DIY Welding - pipewelder

Join Date: Apr 2007
Location: North Georgia, USA
Posts: 671
Good Answers: 33
#9

Re: Motor Operated Valve (MOV)

11/13/2009 4:57 AM

Globe valves (especially motorized globe ) hardly ever stick as long as they are installed with correct flow and stroked every once in awhile. I have seen globe valves stick when installed backwards with the flow because the flow would push against the side of the globe/stem instead of against the bottom and this would in-turn cause it to bend and then stick. I don't think this is your problem though if it works some of the time.

All of the motor valves I have seen the gear reduction gives more torque than most men have unless your guy was using a long valve wrench to help open the valve. You don't tell us what size valve it is or the HP of the motor and if it has a reduction gear so It is hard to say how much torque or HP it would take to close it. I would say it is a near shorted wire, loose connection, bad limits, or some other electrical problem if I had to guess because of the fact that the problem is not continuous.

__________________
pipewelder
Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#10

Re: Motor Operated Valve (MOV)

11/13/2009 8:54 PM

Since I'm more suspicious than most I could tell you that enough out of specs overpressure is a possible reason for a globe valve to refuse to open (but not to refuse to close) as of course is infrequent operation with depositing fluids. All this providing the motor voltage is within specs too.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Active Contributor
Technical Fields - Technical Writing - New Member

Join Date: Mar 2007
Location: Port Sudan
Posts: 16
#11

Re: Motor Operated Valve (MOV)

11/16/2009 1:23 AM

What your MOV actuator type ?

Dose it connected to Master station or stand alone

then you can get good help

Register to Reply Off Topic (Score 4)