When is Neutral Isolation Required?

11/13/2009 5:43 AM

Why and in which application we need to isolate the neutral.

Where are 4P,3P and TPN Breakers used.

Why are generally PCC Incomer and Bus-Coupler Breakers 4P

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Why do we need to isolate the neutral

11/13/2009 8:31 AM

Neutral Isolation is mandatory when you have a Mains Supply Source and a Stand-by Power Supply Source. This is necessary because if you do not have neutral isolation and the neutrals of both the sources are linked, then when only one source is feeding and the other source is OFF, during an earthfault, the potential of the OFF Source's Neutral with respect to earth will increase, which might harm any maintenance personnel working on the OFF source. It is for this reason that PCC Incomers & Bus Couplers are normally 4-Pole. (Note that only either the incomer or the buscoupler need to be 4-pole and not both).

3 pole devices can be used in single source applications, whne the loads do not need a neutral connection. TPN devices in applications which require a neutral connection.

Register to Reply Good Answer (Score 3)
Participant

Join Date: Nov 2009
Location: Thane India
Posts: 4
#3
In reply to #1

Re: Why do we need to isolate the neutral

11/14/2009 4:49 AM

Thanks for the "to the point reply".

But ar there any other implications rather than Commercial if we use 4P for both Incomer and Bus Coupler

Regards

Abhijit

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: Why do we need to isolate the neutral

11/14/2009 5:46 AM

No! Rather, it is much safer to have 4-pole at both Incomers & the bus coupler. But, aren't good engineers good economists too?

Register to Reply
Participant

Join Date: Nov 2009
Location: Thane India
Posts: 4
#7
In reply to #4

Re: Why do we need to isolate the neutral

11/15/2009 10:51 AM

Thanks a lot

Hope our interaction on Electrical Engineering Continues

Regards

Abhijit

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#8
In reply to #1

Re: Why do we need to isolate the neutral

12/04/2009 12:29 PM

Saluting you sir.....very nice explanation.....I had wondered why the buscoupler hav 4 poles......especially given in L&T made PCCs........

__________________
"Know something about everything and everything about something"
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#9
In reply to #8

Re: Why do we need to isolate the neutral

12/04/2009 7:57 PM

Thanks for the compliments! I have also been enjoying your postings in the forum. At this instant, I would like to reiterate that even though I work for L & T, I am not a product marketing person. I only try to explain concepts.

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#10
In reply to #9

Re: Why do we need to isolate the neutral

12/05/2009 8:04 AM

Thank you.....If I could ask can you tell me what are you into in L & T ...how you really get time to reply/opine to the numerous postings in this forum.........But there was no answer to my question in the thread "transformer differential protection".pls reply.

__________________
"Know something about everything and everything about something"
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#11
In reply to #10

Re: Why do we need to isolate the neutral

12/05/2009 8:30 AM

i) I am a Manager-Training with L & T at their Switchgear Training Centre at Coonoor near Ooty in Tamilnadu.

ii) I have a internet connection at home. I am sort of addicted to this forum. And, I sincerely enjoy interacting in the forum. I will not rest for the day unless and until I visit this forum and answer a few questions. Thanks to participants like you.

iii) I have just now answered your query on Transforemr Differential Protection. Please go thro the same and let me have your views on that.

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#12
In reply to #11

Re: Why do we need to isolate the neutral

12/05/2009 1:28 PM

GOOD.......but your knowledge is of high level,to be frank.......keep it up man!

Iam working in petrochemicals/refinery industry as an electrical maintenance engineer for the past 3 years.....

__________________
"Know something about everything and everything about something"
Register to Reply
Anonymous Poster
#2

Re: When is Neutral Isolation Required?

11/13/2009 7:55 PM

Dear sir,

3pole or 4pole switches are used in changing over two independant sources ,where the neutral of one ssource and the neutral of another source should notmix,.the examples are electricity board power supply and standalone generator supply etc. the neutral return current from one source should not mix with or return to another source.

as a mandatory point the neutral of any trabsformer etc are to be earthed,similarly the neutral of a generator also has to be earthed.While paralling (under ubcontrolled condition) the neutral current between the 2 sources will criss cross and create tripping of anyone source breacker.

also as per IECstandard the neutral of a distribution system shall not be earthed more than once.means earthing the neutral further downstream is not correct,

However there are certain conditions under which theAUTOTRANSFER SWITCHES WORKS.The voltage,phase rotation frequency are o be matched for closed loop trancfer. Furthe if interested call"loganathan52@gmail.com"

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus

Join Date: Aug 2009
Location: Gulf Region, IIEE_CRCSA
Posts: 113
Good Answers: 2
#5

Re: When is Neutral Isolation Required?

11/14/2009 11:55 PM

In field practice, in any application on electrical system, neutral needs to be insulated to avoid in contacts or accidental contact in metal parts of the electrical equipement since metal frames are bonded to the grounding sytem. Leakage current current will flow to the path of earthing system will cause a " ground or earth fault current" might harm the working personnel and may even trigger the electrical sparks.

__________________
If there is a will... there is a way... No pain / No gain.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #5

Re: When is Neutral Isolation Required?

11/15/2009 1:54 AM

But the question is Neutral Isolation and not neutral insulation.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13

Re: When is Neutral Isolation Required?

09/21/2023 8:30 AM

The <...neutral...> conductor is current-carrying. Therefore whenever a device is being used for isolation for the purposes of ensuring safety, various standards require it to happen.

It certainly appears in British Standard 7671, for example.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

abhisinkar11 (2); Anonymous Poster (1); electricalexpert65 (5); giri (3); hentoyk (1); PWSlack (1)

Previous in Forum: Electrical Boiler Element Problem   Next in Forum: High Electricity Bills

Advertisement