Energy Efficiency Using VFD and IE2/IE3 Motor Vs. Starter and Standard Motor

11/16/2009 5:01 AM

Can we recomended to used the Variable frequency drive (VFD) with the Energy efficient motor instead of Regular DOL Starter & Standard motor having following advantages:

- The System is rated at 100 % load, however, the motor is loaded up 70 % load, so we can optimised the VFD for 75-80% ( as VFD are direct torque controlled).So current reduction, less cable daimeter (Saving).

-If Three pumps are connected to the bus then Bus bar size reduction, Switch fuse unit (SFU) reduction(saving) & overall transformer rating reduction(saving).

Is it conclude this way. Its an overall integrated system approach with proper sizing of the equipment and Energy efficient solution.

Disadvantages:

- Special cable is required for VFD application.

- The motor ratings (Frame size ) is required comparably one/two size bigger .

__________________
Clean Energy
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Energy efficiency using VFD & IE2/IE3 Motor Vs. Starter & Standard motor

11/16/2009 5:16 AM

Were the installation in the UK, then a combination of approved inverters and EFF1-rated motors would qualify for enhanced tax allowances, meaning that the whole of the installation would qualify for tax relief in the first year, making the installation highly tax-effective and thereby improve its payback time; it makes sense to do it here. For further information on tax-effective energy savings, see the Carbon Trust's website for starters.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Mar 2008
Location: Switzerland
Posts: 17
#2
In reply to #1

Re: Energy efficiency using VFD & IE2/IE3 Motor Vs. Starter & Standard motor

11/16/2009 5:30 AM

Thanks for the Response & valuable information.

This solution is also applicable for UK customers. but what about the overall Capital (installation) cost of such solution in camparison to standard solution.

__________________
Clean Energy
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Energy efficiency using VFD & IE2/IE3 Motor Vs. Starter & Standard motor

11/16/2009 5:39 AM

The capital cost will be higher, clearly, because of the inverter and the possibility of the larger frame size. Given that 20-40% of a country's electricity bill could be related to spinning motors, the installation-life-cycle cost, through using high-efficiency solutions, will be lower.

http://www.abb.co.uk/cawp/seitp202/c1256c290031524bc1256cf7003f391e.aspx

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: May 2009
Location: Centurion, South Africa
Posts: 87
Good Answers: 5
#4

Re: Energy efficiency using VFD & IE2/IE3 Motor Vs. Starter & Standard motor

11/16/2009 6:09 AM

Sorry I don't agree with the larger frame size on vsd motors or eff1 (if I understand you correct). In SA the vsd motors and eff1 motors are in the same frame size and all our lv motors are imported from Europe, Brazil and China..

The only factor that will result in a "larger" frame on a motor driven by vsd is the load and the speed the motor has to deliver the torque (reducing the motor rpm). This may result in a larger motor (higher kW) needed to do the work, but the motor will still remain the same frame size for that specific kW.

__________________
R T F M .......
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Mar 2008
Location: Switzerland
Posts: 17
#5
In reply to #4

Re: Energy efficiency using VFD & IE2/IE3 Motor Vs. Starter & Standard motor

11/16/2009 7:26 AM

For VFD application motor, the speed ratio is for eg. 1:10 i.e 150:1500 RPM, when the motor have to run at 1/10 th speed , more temperature rise will be there. Higher frame size will provide higher air space.Also, fan is provided on the shaft for cooling purpose.

__________________
Clean Energy
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Energy efficiency using VFD & IE2/IE3 Motor Vs. Starter & Standard motor

11/16/2009 12:59 PM

- The System is rated at 100 % load, however, the motor is loaded up 70 % load, so we can optimised the VFD for 75-80% ( as VFD are direct torque controlled).

The amount of energy consumed by an AC motor has to do with 2 things: load and efficiency. So if a motor is only 70% loaded, it is ALREADY going to only pull 70% of the FLC. The losses in the motor will be better with the energy efficient motor design, but if the load is exactly the same in both cases, the VFD will serve only to decrease the throughput efficiency because the VFD adds its own losses. A VFD only saves energy if, in the process of reducing the speed, you reduce losses in the load. A classic example is in a pump system, where the load is normally varied by a throttling valve of some sort. That valve represents a pressure drop and therefore a loss in the load. Eliminating the valve and using a variable speed drive eliminates that loss in the system and saves energy. If there is no reduction in load losses, there is no energy savings with a VFD.

- So current reduction, less cable daimeter (Saving). -If Three pumps are connected to the bus then Bus bar size reduction, Switch fuse unit (SFU) reduction(saving) & overall transformer rating reduction(saving).

Very incorrect! No installation rules I am aware of allow you to down size conductors, be they cables or busbars, based upon actual connected current. they must be sized for the MAXIMUM current, assuming that at some point the motor MAY draw FLC. In fact, here in the US, you are REQUIRED to size the conductors based upon 125% of t VFD's MAX CURRENT RATING, with now allowances for actual load current. So if, for example you use a VFD that is larger than the motor (which is perfectly fine to do), you must still size all conductors as if the VFD were connected to a full load at it's maximum current rating.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Participant

Join Date: Nov 2009
Location: Kakinada, India
Posts: 2
#8
In reply to #6

Re: Energy efficiency using VFD & IE2/IE3 Motor Vs. Starter & Standard motor

11/17/2009 12:27 PM

JRaef..

Ur right.......VFD is no way related with EE motors.......

The puspose of VFD is reduceing in incresing the Speed of motor to control the pump flow......

EE motors construction itself reducing the losses......

i hope m correct its my practical exp...

Reg

Santhosh

Register to Reply
3
Member

Join Date: Nov 2009
Posts: 6
Good Answers: 2
#9
In reply to #6

Re: Energy efficiency using VFD & IE2/IE3 Motor Vs. Starter & Standard motor

11/18/2009 7:50 AM

If I understand the original post, the 70% motor load may be interpreted as 70% power, not current, as both the power factor and the no-load current of the motor come into play. So it will probably not equate to 70% motor current, but somewhat more at a lower pf. If using VFD, the input could be described as 70% power but the current will depend on the harmonic content determined by the power supply and any other optional mitigation techniques employed by the VFD e.g. reactors.

I guess the original post implies that at 70% load the VFD will reduce the voltage accordingly to improve the motor efficiency (if possible) and pf at this lighter load. this may marginally improve motor efficiency although not very significant at only 70% load, particularly if Eff 1 design.

Of course, if these are centrifugal pump applications I assume that no oversizing needs to be implemented for Class F insulation even if reducing speed but many motor suppliers are conservative when selecting for VFD use because of careless setup etc. Furthermore, if there are three pumps, there may be possible energy savings if reduced flow is acceptable under site conditions, this is the potential major energy saving benefit as you very correctly describe..

Direct current control is characteristic of one manufacturer and very similar control is available with most good quality VFD's, normally using one of the various 'Vector' descriptors. They all offer good motor control at partial load.

If useful, many VFD's can offer a current limiter which can effectively limit maximum torque, you can also implement a maximum power limiter too so you can keep at 70% max power if needed. This can be useful if the power supply is limited to save nuisance cutouts etc.

Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Oct 2009
Posts: 15
#7

Re: Energy Efficiency Using VFD and IE2/IE3 Motor Vs. Starter and Standard Motor

11/17/2009 8:21 AM

Implement Demand Controlled Ventilation with the VFD and economizer and get an additional 10% energy efficiency.

__________________
Shinebox
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Aldego (1); Anant Shelar (2); Florence (1); Greg Shine (1); gunalsanthosh (1); JRaef (1); PWSlack (2)