Differences Between Magnetic Contactors

11/19/2009 2:13 AM

I'm an engineer in a switchboard manufacturing company. Sometimes client demand to use AC6b contactor instead of AC3 contactor(commonly used) in capacitor bank . Anyone knows what's the main difference?

__________________
How much better is it to get wisdom than gold and to get understanding rather to be chosen than silver
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Difference between AC3 & AC6b Magnetic Contactor

11/19/2009 3:19 AM

Somewhere in that company will be a standards manual for switchboard design and manufacture. What does it say on the topic?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#2

Re: Difference between AC3 & AC6b Magnetic Contactor

11/19/2009 3:30 AM

These are the duty cycles, there was a previous thread where an explanation was attached. Lazy to search out, try the search feature for it- or look here Page 5.

Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Difference between AC3 & AC6b Magnetic Contactor

11/19/2009 1:11 PM

AC6b is a special purpose contactor specification that requires a "pre-charge" circuit for the capacitors that goes through a 2nd set of "early make" contacts wired to resistors that closes before the main power contacts close, which reduces the capacitor charging current spike that can eat up the contacts and cause other problems in sensitive equipment connected to the same circuit.

If you use regular AC3 rated contactors on capacitors, the contacts will fry in a few thousand operations (as opposed to 1 million) and things like electronic relaying or PLCs will likely suffer premature failure; not good for switchgear.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4
In reply to #3

Re: Difference between AC3 & AC6b Magnetic Contactor

11/19/2009 10:58 PM

GA.

Before the advent of 'pre-switching' capacitor-specific contactors, NEMA ICS2 recommended that one can wind a few turns of the contactor-to-capacitor wire on a 6" mandrel, maybe 6 turns to form an air-cored inductor. This inductor would offer a high impedance to the 15kHz spike that would appear when switching on multiple capacitors. A good common-sense solution. However, now that specifically designed AC6 contactors are available, one must use them.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Differences Between Magnetic Contactors

11/22/2009 4:38 AM

A capacitor's switching inrush transient can be as high as 20 times the rated current and it can last for about 4 to 5 cycles. A magnetic contactor's making capacity in AC-3 is only 10 Ie (Ie - Rated Opertaional Current). So, if you use a AC 3 rating contactor for Capacitor Switching, it will not be able to "make" the switching current and might damage.

A contactor rated at AC-6b - is designed for taking up the effects of the high magnitude of the capacitor inrush.

Alternately, manufacturers sell AC-3 Contactors for Cap. Switching with a set of current limiting resistances in series, so that the inrush current is limited by the resistance and now the AC-3 rated contactor can handle the switching inrush.

I differ with other replies in this post. A contactor with a set or resistors and pre-closing contacts doesn't make it AC 6b. The contactor is still AC 3, but only the current is brought down within it s making capacity. But, if a contactor is designed for AC 6b, it will be able to "make" the capacitor switching inrush without the need for any current limiting resistor.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: Differences Between Magnetic Contactors

11/22/2009 6:59 AM

Any contactor can have an assigned rating as per the utilisation category AC1,2,3 or 4 etc. Its rating will come down as the severity of the application increases. AC 6b happens to be the utilisation category for switching capacitors. Contactors with early closing contacts with current limiting resistors and / or reactors were developed just for this purpose. Needless to say any conventional contactor will also have an AC6b rating, albeit low as one goes into multiple capacitors switching. It may be interesting to note that switching of multiple capacitors can give rise to inrush currents of the order of 180 times the rated current. It is really in such cases that these special contactors make themselves an obvious choice.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); JRaef (1); kvsridhar (2); PWSlack (1)

Previous in Forum: TNS Systems and BS7671   Next in Forum: Voltage Levels as per IE Rules

Advertisement