Selecting Switch Gear and Components

11/22/2009 12:09 AM

I am an architect, and understand some of the principles of three phase power, but.....I am doing a preliminary design and coste estimate for a small industrial building with several pieces of equipment with varing voltage and phases. The equipment list includes 480V 3 Phase, 208V 3 Phase, 208V single phase, and 110V single phase. Total building load appears to be 463 kVA. We are sizing around 600 kVA transformer, 480V 3 Phase 1200A service. In order to serve the various voltages (and phases) Can we get switch gear that steps down inside the cabinet? Or do we need to do something different? If we can't step down in the switch gear, what other components do we need? Thanks for your help!

Bernie

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Jan 2008
Location: Bangalore , India
Posts: 52
#1

Re: Selecting Switch Gear and Components

11/22/2009 12:20 AM

switch gears are protective devices and i dun think it will step down !!

u can use a step down transformer , possibly an autotransformer where ur desired voltage is chosen with winding tapped from the desired value !

__________________
Frank - Catch my statement if you can.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Selecting Switch Gear and Components

11/22/2009 1:51 AM

For 463 KVA, a 600 KVA transformer is a rational choice. You might suffice with 500 KVA, but the extra reserve is probably good. However, 600 KVA ≈ 721 A, which would suggest an 800 A service. Of course, if you are thinking of future expansion, a 1200 A service could later be expanded by increasing the transformer.

The key question here is the size of the 208-120/3 portion of this system. Most likely you would use a stand-alone 480/3 x 208-120/3 transformer. (It needs air circulation around it, which would preclude putting it in the switchboard, unless it is rather small.)

The 208/1 and 120/1 loads can be taken from the 208/3 subsystem (the 3-phase 208 V loads would use 3-pole circuit breakers; the 1-phase 208 V loads would use 2-pole CBs, and the 1-phase 120 v loads would use 1-pole CBs).

Your 480/3 CB switchboard would include one CB to feed the primary of the 480 x 208-120 transformer, which would in turn feed a separate panel with CBs for the 208 V and 120 V loads.

The 480 and 208-120 circuit breaker panels could be integrated into a single enclosure, although I don't recall seeing such a layout myself.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#3

Re: Selecting Switch Gear and Components

11/22/2009 10:44 PM

Bern2009,

The other answer aims you in the right direction. I'll add:

  • The two voltage levels need to be in separate panelboards. None are made that combine them into a single device, and as an electrician, I wouldn't want to be responsible for wiring such a combination (because of safety).
  • Many plants will place the 480/277x208/120V transformer overhead above the panel or disconnect feeding it and with the panelboard it supplies directly below. This minimizes consumption of floor space.
  • I'm surprised that you don't have an electrical engineer consult on even a preliminary design and cost estimate. He/she would be able to keep you from any serious errors at this early date.

I wish you well--John M.

Register to Reply
Anonymous Poster
#5
In reply to #3

Re: Selecting Switch Gear and Components

11/23/2009 4:50 AM

i would add have you checked the diversity factor before zeroing on the Transformer size you have selected and what about backup generator requirement sizing?

good luck

crm

Register to Reply
Associate

Join Date: Sep 2009
Location: Medan - Indonesia
Posts: 34
#4

Re: Selecting Switch Gear and Components

11/22/2009 10:52 PM

bern2009,

I don't understand how on earth can an architect now handle the electrical things.....

My suggestion is ,GO FIND AN E.ENG Because THIS IS NOT YOUR DOMAIN !!!! tq

__________________
A Wise Man changes his mind, a fool never will
Register to Reply Score 1 for Off Topic
Anonymous Poster
#6
In reply to #4

Re: Selecting Switch Gear and Components

11/23/2009 4:52 AM

i would appreciate at least he is asking instead of messing up every thing on his own as it happens now a days

crm

Register to Reply
Anonymous Poster
#7

Re: Selecting Switch Gear and Components

11/23/2009 2:01 PM

As mentioned in earlier posts,because of the cooling it would not be posible to enclose transformer internally, your choice of 600kVA transformer is sufficient but not ample should there be a requirement to increase the loading.

Cheers

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#8

Re: Selecting Switch Gear and Components

11/23/2009 3:03 PM

Hi Bernie, and welcome to CR4.

With a 480V service, you would need a 277/480V to 120/208 3 phase transformer for the lower voltage loads. It's possible to build that into the 480V switchgear, but it would be a custom design. If you're in the US, it would require approval of the local inspection authority (usually the electrical inspector for the city or county Construction Services Dept.).

The 480V and 208V circuits would need to be in separate cubicles meeting NEMA and NEC requirements. For more information, I would recommend contacting switchgear manufacturers. I have used Eaton, Square D, Powell and Myers Controlled Power for custom designs with great success.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Participant

Join Date: Nov 2009
Posts: 2
#9

Re: Selecting Switch Gear and Components

11/23/2009 7:46 PM

Thanks everyone... I have what I need.

To Tootje: Be assured that I intend to include an Electrical Engineer. I like to know (at least in concept) what's included in the project before I start. Owners have a tendancy to purchase (or budget ) an equipment package before they know their options. In this case, the vendor has proposed an equipment package. I'm just trying to understand what's required so I can relate to the owner, and maybe simplify things before I activate the design team.

Not an EE wannabe

Bernie

Register to Reply
Associate

Join Date: Sep 2009
Location: Medan - Indonesia
Posts: 34
#11
In reply to #9

Re: Selecting Switch Gear and Components

11/26/2009 9:14 AM

Hi Bernie,

Based on your lack description, let me try to give you my opinion

  1. list down 480V/3P loads
  2. lists of 208V/3P load equipments
  3. lists of 110V/1P loads

in case 110V/1P loads are not so big, then you may put the 208V/110V step down transformer in a cubicle. In short ,what you need are :

  • 1 ea switchgear with 1 incomings 800A ACB outgoings depends on how many loads plus CB to 480V/280V transformer & spares. (1200 A is too big & you have to invest with bigger dimension of cable)
  • 1 ea 600 kVA 480V/208V transformer
  • 1 ea ? kVA 208V/110V transformer
  • as I stated above, if your 110V/1P loads are not significant then the 208V/110V step down transformer may be put in a separate cubicle in the switchgear, otherwise you have to pull cable from the switchgear to feed this Tf and
  • you gotta provide another 110V distribution Panel with 1 incoming dependant with Tf capacity and several outgoings

thank you & may this can help.

__________________
A Wise Man changes his mind, a fool never will
Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#10

Re: Selecting Switch Gear and Components

11/24/2009 11:48 AM

Though an auto xformer wt multi tappings is neccessary for this project,wt custom built design into a SG Panel,we must consider deeply,sizing of d xformer for d 3 phase 480v and 3 phase 208v.If d 480v gives 721.709A,would not d 208v give 1665.48A?

In a 3 phase ac netwk under load,voltage and current are in inverse proportion.Are we using seperate xformers for d 480v and 208v 3 phase or single multi tapping? We need to consider deeply if using single multi tapped xformer can handle d load,and at what kva and current rating for d 480v and 208v,3 phase.Well,for 480v,3 phase,600kva xformer at 721,7A(800A) is ok,but what about 208V,3 phase?

Lets remind us as well that 2.2kw(230v) single phase motor or pump will draw a higher current than 2.2kw(400v) 3 phase motor or pump.Its all for our discussion and consumption.

Patrick Whowha

__________________
Patrick Whowha
Register to Reply