Hello guys, since last 2 days, i'm having problem with my aux generator for our installation offshore. The driver is CAT engine diesel fuel if i'm not mistaken it's D 3416 model. The rated power is about 1.3MW.
the problem now, the engine trip without indication on my Local panel ( its control by PLC : OMRON and power manage by WORDWARD (sync and load) system.
I've tried to inhibit all the tripping switch, low2 lube oil, rigsaver,Temp high2. the engine still trip after 1/2 hour. even manually closed the switch loop to ensure its alway energize. still failed.
There is no problem with the load, confirm by recheck and rewired back all the ACB, initially was suspected the reverse power.
i've simulated all the communication between the OMRON PLC to the ECM. for START/STOP and Emergency stop.. it working fine, Start the engine with jump this signal still the engine trip..
now the only suspicious culprit is the ECM module, since i've confirm all the engine head/ injecter working fine. there is no sign of misfire and hammering sound.
the question is anyone of you guys ever experience this? the worst thing is i cant find any model/spare no/ part no/ on that ECM which consist of electronic board..
thanks for reading :)