Hazardous Area Electrical Installation

11/24/2009 12:23 AM

Hello All,

Can using Steel Wire Armoured cables cancel out the need of using IS Barriers completely. I am involved in designing and installation of Electrical and Instrumentation at one distillery. Because the product is hazardous (with some flash point which I dont know) there were barriers installed on all the 2 wire instruments before the PLC I/O cards on the old distillation columns. But now I have been told to install SWA cables without barriers for all the instrumentation for a new project. What can be the reason or am I missing out some thing??

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Hazardous Area Electrical Installation

11/24/2009 3:15 AM

<...involved in designing and installation of Electrical and Instrumentation at one distillery...>

Stop!

Request training in the design process and attend the training course before carrying out any modification to the old or the design of the new installation. This is a topic that requires a level of training, and the nature of the posted question indicates that the poster is not yet able to apply this training to the tasks to be done.

Either that, or delegate the task to someone else that has.

The nature of the flammable material needs to be known so that the correct temperature class and gas group can be specified for the selection of new equipment.

The facility requires a zone classification drawing so that correctly zone-rated equipment may be selected for the appropriate areas.

<...been told to install SWA cables without barriers for all the instrumentation for a new project...>

This would be correct only if all the equipment in the hazardous area is EEx d, e, p, N or o and any junction boxes in the hazardous area were either EEx d or EEx e. Barriers are only used for installations that fall under EEx i.

Did the person that made this suggestion mention anything about the glands to be used under EEx d?

http://en.wikipedia.org/wiki/Electrical_Equipment_in_Hazardous_Areas

The correct installation method is also coloured by national electrical codes. An installation on the North American continent would differ from one that does the same job on the European continent, for example.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 3)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Hazardous Area Electrical Installation

11/24/2009 9:59 PM

Can using Steel Wire Armoured cables cancel out the need of using IS Barriers completely

Not in any American ATEX or European IEC standard I am aware of. Armouring of the cable is not acceptable on its own as a substitute for a purely intrinsic safety protection.

What can be the reason or am I missing out some thing??

Perhaps the equipment in the hazardous area is being installed in Ex d flame proof or Ex p pressurised enclosures (which provides the level of protection necessary instead of Ex i intrinsic safety). Perhaps the PLC I/O has an intrinsic safety rating and so doesn't require the additional barriers the old installation had (this is more common nowdays).

Since there could be a number of valid reasons for this perhaps you should ask the site system design engineer (or whoever is in charge of the hazardous area design), we can only guess (which is never a good idea when hazardous area design is involved).

__________________
jack of all trades
Reply
Anonymous Poster
#3
In reply to #2

Re: Hazardous Area Electrical Installation

11/24/2009 10:49 PM

Thanks for the info. May be I will check the PLC I/O. But out of curosity,in general will SWA cable prevent arching or is it just for the sake of durability.

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5
In reply to #3

Re: Hazardous Area Electrical Installation

11/25/2009 1:06 PM

SWA cable is common on hazardous area sites and is used to provide an extra level of cable protection compared to unarmoured or unscreened cable. Its use really depends on the application, cable position, existing cable protection (cable tray/cable conduit, etc) and site-specific and company standards.

__________________
jack of all trades
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #3

Re: Hazardous Area Electrical Installation

12/01/2009 7:14 AM

It's there to give mechanical protection to the cable. There is no absolute need to use it. One could use various styles of conduit instead, for example.

There would be no incendive sparks were the cable to be correctly installed on an EEx i circuit, whether subjected to mechanical abuse or not.

The PLC I/O is irrelevant.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Associate

Join Date: Oct 2009
Posts: 33
#4

Re: Hazardous Area Electrical Installation

11/25/2009 5:08 AM

Hi,Guest,

Quite apart from any governmental standards requirement regarding cabling,glands,junction boxes etc. - the whole idea of Intrinsically Safe Barriers is to prevent ANY Voltage/Current combination reaching the instrumentation/control gear within the hazardous area. Steel-shrouded cable will not prevent sparking or overheating if, say, 12v DC finds it's way back from a defective temperature controller to a thermocouple element. Look at the original installation with this in view - you'll see why the I.S. barriers were fitted in the first place.

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #4

Re: Hazardous Area Electrical Installation

12/01/2009 7:17 AM

The original poster hasn't mentioned the protection concept of intrinsic safety so far.

Intrinsic safety is not confined specifically to 12VDC circuits. 28VDC is possible within the hazardous area under EEx i, for example, as would be a range of AC systems.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: Oct 2025
Posts: 1
#8

Re: Hazardous Area Electrical Installation

10/28/2025 8:48 AM

That’s a very valid concern. Using Steel Wire Armoured (SWA) cables does not cancel out the need for intrinsic safety (IS) barriers on its own. The SWA cable mainly offers mechanical protection and grounding, but it doesn’t limit electrical energy, which is the key function of IS barriers in hazardous areas.

You might have been advised to omit barriers because the new installation could be designed under a different protection concept, such as Ex d (flameproof) or Ex p (pressurised). These systems contain or isolate potential ignition sources, allowing higher energy levels without the need for barriers. However, this is only valid if every device, enclosure, and junction box in the hazardous area is appropriately rated for that protection type.

In similar industrial setups managed by Electrician Singapore, engineers first perform a hazardous area classification and confirm all protection methods before installation. This ensures compliance with local and international safety standards, especially in facilities handling flammable or volatile materials.

It’s strongly recommended to review the project’s hazardous area drawings and confirm with the design or safety engineer before proceeding. When it comes to explosive atmospheres, verifying every protection method is essential to maintaining both compliance and on-site safety.

Reply
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); jack of all trades (2); matthewhughes (1); PWSlack (3); Zadok (1)