Anonymous Poster

MCC Busbar Size Requirement

11/30/2009 4:36 PM

Per UL845, would an MCC with a 2000Amp horizontal bus be able to feed four 400hp motors all running at once (@480Volt)? Please spell out any codes referenced from UL845 because I do not have the book.

FYI:

- Running load is 1908A

- MCC bus sizing requirements is not contained in NEC (NEC only deals with regular conductor sizing, mostly insulated conductors)

- UL845 contains busbar sizing, but I do not have the book.

Thanks, Bishop.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: MCC Busbar Size Requirement

12/01/2009 6:33 AM

It sounds as though buying the book is the first step, perhaps?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#2

Re: MCC Busbar Size Requirement

12/01/2009 7:46 AM

If you are building electrical equipment you need more than just the UL book. What are you going to do about bracing?

Rule of thumb.

1 square inch is good for 1000 amps.

Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#3

Re: MCC Busbar Size Requirement

12/01/2009 10:48 AM

It is nt advisable and may nt feed it conveniently for a period of time.U need to do little calculation on yr current carrying capacity of cables and or bursbar to get a good long time result.

Yr total full load motor current may be say 1804.4Amps,but other loads may raise it up to 1908Amps.Each time u start there is always more current drawn b4 the motors stabilize.The bursbar is equally affected gradually.U nd to add say 25% tolerance(25% of 1908=477).1908+477 gives 2385Amps.Look for the next available standard bursbar rating which could be about 2500Amps or thereabout and install this to conveniently carry yr loads for a reasonable period of time.Use good quality copper bursbars.

Patrick Whowha

__________________
Patrick Whowha
Reply