11/30/2009 6:28 PM
Please give the short circuit current in single phase 230V
And short circuit current in three phase 415V
Arun Babu
Re: Short Circuit
11/30/2009 6:37 PM
arunbabu,
The more information the better the answer.
Short-Circuit Calculation Methods
Re: Short Circuit
11/30/2009 6:59 PM
It is apparent that you have never had to make this calculation. You have provided none of the information required. Lyn has provided you a good method to make this calculation. Let us know how you come out.
Re: Short Circuit
12/01/2009 4:36 AM
The short circuit current is depending on the total impedance of your system.
Simply divide your voltage to the total impedance of your system. The result is your short circuit current.
Kindest Regards
Re: Short Circuit
12/01/2009 7:06 AM
data is inadequate
Re: Short Circuit
12/02/2009 6:46 PM
for 230V, Isc = 230/ short circuit resistance
for 415V, Isc = ( 1.732 *230)/ short circuit resistance for 1phase fault