Buchholz Relays

12/02/2009 6:26 AM

as i've read some articles & threads regarding these,bucholz relay has 2 mercury switch, 1st is the slow accumulation of gas due to internal faults inside the T/R which gives the alarm & 2nd is the rapid accumulation of gas & oil surge from the main T/R tank to the conservator which trips the T/R & open the breaker.how does the oil from the main tank go to the conservator?what is the primary function of the conservator?how does bucholz relay operates?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: Buchholz Relays

12/02/2009 8:58 AM

Start with this article on Wikipedia.

Reply
4
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Buchholz Relays

12/02/2009 11:46 PM

The primary function of the conservator is to provide space for the expansion of the oil in the transformer main tank during loading related heating of the oil. The Buch Holz Relay is mounted in a pipe from the transformer main tank to the consevator. The pipe is intentionally kept at a slope of about 2 to 7 degrees. As the oil in the transformer tank expands during loading or during faults, it finds its way to the conservator thro this pipe & the relay. As the pipe line is sloped, any gas accumulated is collected at the top of the pipe & the relay. As long as the volume of gas collected is within limits, nothing happens. But during incipient faults inside the transformer, the decomposition of oil and hence the gas collection is rapid that much volume of gas is collected in the relay. As the volume of the gas collected increases it pressurises the relay chamber and presses down the oil. The slantingly kept mercury switch straightens out and the mercury now links the two terminals, thus closing the contact. As you have rightly pointed out, the top mercury switch is for alarm and it gets activated first. But, if you ignore the alarm and the fault persists further gas accumulation will also push down the bottom mercury switch to trip the supply to the transformer, provided the logics are properly wired for the purpose.

Reply Good Answer (Score 4)
Anonymous Poster
#3
In reply to #2

Re: Buchholz Relays

12/30/2009 10:27 AM

Excellant ans.