Anonymous Poster

diesel generator power factor

12/03/2009 5:35 PM

how to calculate the power for prime rating 1200Kva generator at 55C and altitude of 600m?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: diesel generator power factor

12/03/2009 7:31 PM

The load determines the power factor. If you have a load such as electric heating, the PF = 1. If you have motors the PF might be 0.80.

Reply
Anonymous Poster
#2

Re: diesel generator power factor

12/03/2009 9:17 PM

Usually the generators do not need derating for 1000ft or so, after that as I remember 2-5% derating is recommended for every 1000ft.

Derating is also required for ambient above 400C (cooling, air density, humidity, etc all matter). For 550C it may go as low as 90% (ie DRF=0.9)

Unfortunately both these parameters are design specific and hence not only manufacturer but also model dependent. Since it all depends on how that air is utilised, how the heat is dissipated and the capacity of the machine to withstand heat.

The actual answer may be obtained from the manufacturer

for example

Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: diesel generator power factor

12/03/2009 9:42 PM

I thought your question was about power factor.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: diesel generator power factor

12/04/2009 8:48 AM

Please note that the alternator loading is in Amperes and the Diesel Engine loading is in HP. So, control alternator loading by monitoring the ammeter and control the engine loading by monitoring the kW meter.

Reply
Power-User

Join Date: Oct 2009
Location: Istanbul. European side
Posts: 151
Good Answers: 4
#5

Re: diesel generator power factor

12/04/2009 2:44 PM

It is very clear that the question is how to calculate engine + alternator de-rating at the said ambient conditions.

I have worked many years with generator design and calculations.

Engine derating is different from manufacturer to manufacturer, for the same power.

Derating can be different for each engine, even the same manufacturer's product . If the engine is turbocharged, derating is different, In the cases the charge air is Inter/aftercooled, derating also varies.

The only reliable way how to calculate derating for a certain engine is to refer the leaflets of the manufacturer's laboratory tests. Diagrams on the engine's own leaflet is indicating the power decrease in altitude and ambient temperature variations. Values are extracted from real test results.

The same logic is valid also for the alternators. Altitude is effective on the cooling air of the alternator (The cooling air is thin in the high altitudes, therefore cooling is poor), as well as the ambient temperature.

You must refer the manufacturer's test reports and must take both the engine and the alternator deratings into consideration for your own ambient conditions.

Kindest Regards

Reply Score 1 for Good Answer
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); nezihozfirat (1); wareagle (2)