Why there is only one undervoltage coil across any 2 phases instead of 2 coils across 3 phases.How its able to detect the undervoltage in other phase where there it's not connected to the coils???hope somebody can help me out here.............
"Know something about everything and everything about something"
Re: Undervoltage relays
12/04/2009 11:55 AM
one coil can detect under voltage of connected phase two only ,for monitoring all three phase you need 2 coil,
Good Answers: 804
Re: Undervoltage Relays
12/04/2009 2:50 PM
UV relays are supposed to protect equipment, most often motors, from the dangerous effects of continuous under voltage conditions. But sometimes, they are used only to detect a complete power outage. So if that is the purpose, sensing only 2 of 3 phases may be sufficient. Not advisable, but sufficient if one of your other criteria involves being too cheap to pay a little extra for a 3 phase monitor.
But are you referring to UV coils in a circuit breaker? If that's the case, they are used not as UV monitors but as control devices that respond to a REMOVAL of control power rather than a APPLICATION of control power (as a Shunt Trip does).
Good Answers: 170
12/05/2009 4:23 AM
Economy boss! In a three phase system one phase undervoltage is a very rare phenomenon. So, if you can monitor the voltage of any two lines (one phase) that would be sufficient.
However, if single line to neutral undervoltage is anticipated - may be due to improper load distribution in a three-phase 4-wire system - you can always go for three single phase undervoltage relays.
Good Answers: 61
12/07/2009 10:03 AM
The UV coils are connected phase to phase, and sense the potential difference between the phase conductors. Consider a single UV coil connected between phases A & B. A low voltage in phase A will lower the voltage across the coil, causing it to de-energize. Likewise, a low voltage in phase B will also lower the voltage across the coil, also dropping out the coil. That single coil monitors both phases.
Connecting 2 coils will provide complete phase undervoltage protection, as long as each phase is connected to at least one coil. Two coils provide 4 points of connection, so one phase will be common to both coils.