Previous in Forum: How to Estimate Residential Kilowatt-Hours (kWh)   Next in Forum: Power Cable and Incorrect Inlet Pressure
MCC Panel Current Carrying Capacity
12/07/2009 1:57 AM
dear all,
i need to calculate a current carrying capacity of incoming MCCB for a MCC panel
as per IEC standard
datails:
we have 10 branch circuits of each capacity 25kw
voltage:3ph,415v
can any one suggest me regarding this and IEC stardard code
rkram
Pathfinder Tags: MCC circuit breaker
Re: MCC Panel Current Carrying Capacity
12/07/2009 3:32 AM
There is an existing thread running on this topic.
Good Answers: 15
12/08/2009 3:52 AM
refer IEC 61439 and if it is not clear then do come back to the thread
12/08/2009 10:18 PM
can you tell the IEC standard formula for the calculation of Incoming rating of MCC panel
12/08/2009 10:25 PM
dear sir,
i am using the following formulae to calculate the Incoming rating of MCC panel
NOT Less than Incomer current rating = 25% of full load current of largest motor + Full load current of remaining motors
and
NOT More than Incomer current rating = 250% of full load current of largest motor + Full load current of remaining motors
I have selected inbetween the above ratings.
Please tell me am'i following the IEC standard
can you give the IEC standards document related to this MCC rating calculation
please help me.
Thanks,
with best regards,
rkram
10/11/2021 4:25 AM
Invitation declined.
10/11/2021 4:32 AM
<deleted comment>
12/09/2009 2:54 PM
If u ask me,i would simply help u to calculate yr MCCB incoming current rating.
Yr total load is 250kw(assume full load).P=root3VIcosO,O is phi.I=P/root3VcosO=250000/1.732x415x0.8=250000/575.024=434.76Amps. Multiplying 434.76 by a factor based on regulation(check yr Regulations on protective devices calculation),you will get 782.57Amps,then select MCCB range of 800Amps.
This will carry and protect yr total loads conveniently if u get a quality ABB/MITSUBISHI or other quality breakers.
Patrick Whowha
Patrick Whowha
Register to Reply 7 comments