Busbar Calculation

12/07/2009 3:12 AM

can anybody help me out regarding busbar calculation

i hv 100A copper busbar and its cross sectional area is around 50mm square. so i need 2 find the short time withstand current for this 100A copper busbar system.

if u hv any solution regarding this pls help me ...

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: how to calculate short time withstand current for busbar

12/07/2009 3:26 AM

http://cr4.globalspec.com/search/sitesearch?do=show&sort=textmatchrank&srch=busbar%20sizing&order=asc

It's one of CR4's favourite topics (the other is cable sizing, for which the answer is British Standard 7671).

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: how to calculate short time withstand current for busbar

12/07/2009 8:58 AM

The formula is:

K2S2 = I2t (K square S square = I square t)

Where,

S = Cross section of the conductor, in sq.mm

I = Short circuit current in Amperes

t = With stand time, in seconds

K = Constant, depending upon the material of the conductor, insulation & type of installtion, etc. (Defined in IEC)

Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#3
In reply to #2

Re: how to calculate short time withstand current for busbar

11/21/2011 5:52 AM

Expert65,

why in somecase, there is still written value of peak s/c current ?

for example :

we have got value of rms Short Circuit (s/c) = 25 kA

the peak value is 2.7*25 kA = 68 kA

the peak value is to determine breaking capacity of CB.

the rms s/c value is to determine thermal withstand of busbar and CB.

then, question in my head, is there another choice for CB selection , if we have got rms value 25 kA then there is not automatically we chooce CB with breaking capacity 68kA ?

pls help me to explain it.