can anybody help me out regarding busbar calculation
i hv 100A copper busbar and its cross sectional area is around 50mm square. so i need 2 find the short time withstand current for this 100A copper busbar system.
if u hv any solution regarding this pls help me ...
Re: how to calculate short time withstand current for busbar
12/07/2009 3:26 AM
http://cr4.globalspec.com/search/sitesearch?do=show&sort=textmatchrank&srch=busbar%20sizing&order=asc
It's one of CR4's favourite topics (the other is cable sizing, for which the answer is British Standard 7671).
Good Answers: 170
12/07/2009 8:58 AM
The formula is:
K2S2 = I2t (K square S square = I square t)
Where,
S = Cross section of the conductor, in sq.mm
I = Short circuit current in Amperes
t = With stand time, in seconds
K = Constant, depending upon the material of the conductor, insulation & type of installtion, etc. (Defined in IEC)
11/21/2011 5:52 AM
Expert65,
why in somecase, there is still written value of peak s/c current ?
for example :
we have got value of rms Short Circuit (s/c) = 25 kA
the peak value is 2.7*25 kA = 68 kA
the peak value is to determine breaking capacity of CB.
the rms s/c value is to determine thermal withstand of busbar and CB.
then, question in my head, is there another choice for CB selection , if we have got rms value 25 kA then there is not automatically we chooce CB with breaking capacity 68kA ?
pls help me to explain it.