Hello,
What will happen if I use 1 pair instrumentation cable to supply 2 transmitters (4-20mA)??
Re: 4-20mA
12/09/2009 3:52 AM
Nothing useful will come out of the cable at the receiving end.
Re: 4-20mA
12/09/2009 4:24 AM
what would be the point in that ??? how would you connect the transmitters in parallel or in series ? weird question !!
Do you not mean a valve positioner ??
United States - Member - US Citizen - Born & Raised Engineering Fields - Control Engineering - HVAC/R Simplified Using PLC Controls Engineering Fields - Instrumentation Engineering - HVAC/R Simplified Using PLC Controls Engineering Fields - Energy Engineering - HVAC/R Simplified Using PLC Controls
Re: 4-20mA
12/12/2009 10:52 PM
Is the cable providing power to the transmitter or is the cable returning a 4-20mA signal from two sources?
1. If power, nothing. This will be fine to supply the transmitters with power from the same source if 4-wire transmitters. It should not be used with multiple two wire current loops.
2. Never could you share the signal from two transmitters on one pair of wires.