System Neutral and Earth Bus

12/08/2009 11:10 PM

I have seen 2 earthing for 415 V TPN System

1) System Neutral & Earth bus shorted in the Switchboard & finally earthed at one place

2) System Neutral & Earth bus are kept separate & earthed separetely at 2 different places

So what is the advatage& disadvatage of 1st over other

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: System Neutral & Earth bus

12/08/2009 11:15 PM

This has been covered in earlier CR4 threads, pleas search.

technically the shorting of neutral awith earth is not preferable at user level, nor most of the codes permit this. This is due to the alternate path created to the earth fault to flow through (and also the neutral current will have now two paths to follow, bot at equipotential.

Also it will have a bit problem at substation level, where the neutral is shorted with/without NGR.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: System Neutral & Earth bus

12/09/2009 3:40 AM

Please read the article on earthing systems in Wikipedia.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Sep 2009
Location: INDIA
Posts: 92
#3

Re: System Neutral & Earth bus

12/10/2009 4:16 AM

As earthing is connected to earth the equipment body ,where as neutral is connected for fault current to flow in fault condition means current carring.

Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#4

Re: System Neutral and Earth Bus

12/10/2009 6:00 AM

We have PE and PEN systems of earthing.

PE is protective earth,which is a seperate earthing method.No neutral is combined.

PEN is protective earth and neutral,where earth and neutral is linked or combined.

Some use PEN and some use PE on their installations,depend on which method is most suitable for your method of installation.Pls,read yr books on protective measures or yr regulations and you will get the best answer to yr question.

Knowing fully well that neutral is a return path for healthy current which goes back to source,earth is a return path for fault current(earth fault) which goes to ground(general mass of earth).

Read more and understand yr earthing system to apply,but in most cases,PE(seperate earthing) is used.

Patrick Whowha

__________________
Patrick Whowha
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: System Neutral and Earth Bus

12/10/2009 7:41 AM

If you are bonding the earth and the neutral "also" at the switchboard apart from at the source, then you are violating the law of the land. You are not permitted by law to do so. If you are bonding the earth and the neutral only at the switchboard, then this also is against the Code, as neutral has to be bonded to earth only at the source end and not at the load end.

Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#6

Re: System Neutral and Earth Bus

12/10/2009 10:32 PM

Dear all,

1) If the switchboard is the first switchboard from the transformer, this is correct.

2) This is permitted, if your area allows TT system. The regulations for TT system must be followed.

Advantage of 1) over 2)

Against earth-faults

1) is TN system, OCD overcurrent protection also protect the circuit against earth-faults. 2) is TT system and if the earth resistance between two separate earth electrodes is not low enough, overcurrent protection device will not trip on an earth-fault, thus you need additional RCDs (earth-fault or earth leakage relay).

Immunity to nearby lightning strike

1) Transformer and switchboard is equipotential against lightning. 2) Transformer and switchboard may have hight potential difference, which may break the insulation of both transformer and switchgear.

Advantage of 2) over 1)

Earth-fault current in 2) is smaller than in 1). This is the main advantage of 2) over 1). Facility damage by earth-fault in 2) is smaller than in 1). Voltage dip during an earth-fault is smaller in 2) than in 1).

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Commentator

Join Date: Aug 2011
Posts: 76
#7
In reply to #6

Re: System Neutral and Earth Bus

08/24/2011 1:49 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Off Topic (Score 5)
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

Akihito Shigeno (1); Anonymous Poster (1); electricaleng (1); electricalexpert65 (1); luv123 (1); Patrick Whowha (1); PWSlack (1)

Previous in Forum: lci   Next in Forum: VVVf Drives and Slip Ring Motors

Advertisement