Net Positive Suction Head Available (NPSHA)

12/13/2009 4:52 AM

Hi gents

Is the pressure gauge reading at pump suction equals to NPSHA? on closed system

Register to Reply
Pathfinder Tags: npsha
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: pump question on NPSHA

12/13/2009 5:00 AM

Look here first line

This is one of the better sites on pump.

And there is the explanations for next few pages.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Location: I'm outa here
Posts: 1924
Good Answers: 196
#6
In reply to #1

Re: pump question on NPSHA

12/13/2009 11:00 PM

All you guys bookmark McNally's site. He has most of the answers to commercial size centrifugal pump user questions.

Ed Weldon

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Net Positive Suction Head Available (NPSHA)

12/13/2009 9:04 AM

Depends where the pressure tap is and the configuration of the inlet plumbing.

But, if the pressure tap is at the inlet of the pump it will be close.

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#3
In reply to #2

Re: Net Positive Suction Head Available (NPSHA)

12/13/2009 12:54 PM

By definition- NPSHA reads in absolute values. I know of no gauge that has a readout in absolute pressure.

You would have to add 14.7 PSI (or 1 BAR or 760 mm Hg), assuming you are at sea level, to the actual gauge reading to get a "reading" in absolute pressure. Or, have I missed something?

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Power-User

Join Date: Feb 2009
Location: India
Posts: 155
#8
In reply to #3

Re: Net Positive Suction Head Available (NPSHA)

12/14/2009 4:31 AM

NPSHA is NPSH available. NPSHR is NPSH required.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#11
In reply to #3

Re: Net Positive Suction Head Available (NPSHA)

12/14/2009 10:10 AM

Hello Energygod

Yes, you have . Also need to subtract the vapour pressure of the liquid (as sv13 mentioned) and add the velocity head (using velocity at the pressure tapping point). If you ignore velocity head it gives you a slightly safe (i.e. low) figure for NPSHA, but strictly speaking it should be included.

Cheers.........Codey

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Net Positive Suction Head Available (NPSHA)

12/13/2009 8:45 PM

Absolute pressure gauges exist (many Web references to them), but it is surprising they aren't more commonly used. Compound pressure gauges (measuring pressure above atmospheric and vacuum below) are common, notably in refrigeration, but for some calculations you need to convert vacuum (inches Hg) into equivalent psi units (or the corresponding metric units in either case).

Pressure transducers are also available in absolute units.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Jun 2009
Location: Between India & Australia
Posts: 71
Good Answers: 3
#5

Re: Net Positive Suction Head Available (NPSHA)

12/13/2009 10:58 PM

Not quite. For calculating NPSH, you'll have to sustract the vapor pressure at the operating temperature. If the suction is from a vessel which is at saturated vapour pressure, for example deaerators, then a pressure gauge installed on the pump suction will give a good indiaction of the NPSH avaialble after adding the atmospheric pressure.

It does not matter whether the system is closed or not.

__________________
Continuous Learning
Register to Reply
Commentator

Join Date: Nov 2009
Posts: 78
Good Answers: 9
#7

Re: Net Positive Suction Head Available (NPSHA)

12/14/2009 2:29 AM

Dear Naif,

NPSHA or net positive suction head available is defined this way:

NPSHA = P + Z -hf - hvp

where p is the suction drum pressure, Z is the elevation (differential), hf is the friction loss and hvp is the vapor pressure. All are in unit of length e.g. meter of fluid

When the system is closed, the pressure reading at the suction is the gauge-pressure due to elevation plus the pressure of the suction drum (or P + Z). So in order to find the NPSHA, you need to firstly convert this pressure into absolute term and deduct friction loss and vapor pressure at the operating temperature. Express all terms in unit height of liquid.

In some cases, such as distillation column, the suction drum pressure is equal to the vapor pressure. so the formula for this case is

NPSHA = Z - hf

I some design, the suction friction loss is comparatively small, so in the case the NPSHA can be approximated by

NPSHA = Z = [suction pressure] - [drum pressure]

Hope u get the idea.

Register to Reply
Power-User

Join Date: Feb 2009
Location: India
Posts: 155
#9
In reply to #7

Re: Net Positive Suction Head Available (NPSHA)

12/14/2009 4:38 AM

If the pressure gage is near the suction nozzle, the drum pressure and liquid lift will be included in the gage reading. Only Hf and hvp are to be accounted. Right?

Register to Reply
Commentator

Join Date: Nov 2009
Posts: 78
Good Answers: 9
#10
In reply to #9

Re: Net Positive Suction Head Available (NPSHA)

12/14/2009 4:48 AM

Dear b.v. rao

Yes! you got it right.

If we measure the suction pressure with flow available then the gauge pressure measures the drum pressure plus elevation (or what u called lift) minus the friction loss. So in this case we can calculate the NPSHA by this formula

NPSHA = [suction pressure] - [vapor pressure]

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers: