Valve / Actuator Air Consumption

12/13/2009 6:46 AM

For Air consumption requirements how we can find the Valve Travel takes place in (One minute )--- since it is depends on the process Disturbance

Regards

Jose John

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Valve /Actuator Air Consumption

12/13/2009 8:04 AM

It is not very clear what you want to ask....pls explain in detail....else we cant answer properly

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Valve / Actuator Air Consumption

12/13/2009 9:08 AM

Not too sure here, but I'd pose this question to a valve supplier who speaks your language.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#3
In reply to #2

Re: Valve / Actuator Air Consumption

12/13/2009 9:19 AM

Or may be you should be able to understand valve dynamics first before putting this brilliant answer

Register to Reply Score 1 for Off Topic
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#4

Re: Valve / Actuator Air Consumption

12/13/2009 10:27 AM

It depends on pressure, resistance from spring if present and from flow forces, on seals friction (type, material, lubrication,..), on valve design and several other factors and of course how big is the area of the controlling valve (pilot) or mass of moving equipment....and so on!

The flow as function of above mentioned variables can be sub-critical or critical if pressure drop at pilot valve is under or over the critical threshold. At the stroke end the flow is sub-critical if the sum of resistant forces is big with respect to the pressure force.

As you see even if one looks at details with respect to dynamics of a piloted valve the answer is not simple and the only correct way is to make a full simulation of the system and get from it the displacement-time curve for a given supply pressure.

From an other point of view the valve is in a control loop and will react to the disturbance amplitude and at the settings of your controller (PID or other types) so that if you do not know the transfer function of the valve it is at least very difficult to estimate its reaction.

Register to Reply
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#5

Re: Valve / Actuator Air Consumption

12/13/2009 2:09 PM

Actually Our Mech Discipline engineers need to do the sizing for Air Compreessor they want the total air consumnption for all the valves .

Vendor has sized the valve and actuator and has provided the Voulme of Actuator ,

Based on which I can find the consumption for 01 stroke , But my problem is that I want Consumption for 01 min (SCFM), HonestLY I dont know how many strokes it will do in 01 min .I have asked the licensor for the details Apart from saying Continous Service I am not able to gather much data .

2) May I also know how accurate Thumb Rule is (10 SCFM/Valve)

Pity Some People depend on all the inputs from Vendor side

Regards

Jose

Register to Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#6

Re: Valve / Actuator Air Consumption

12/13/2009 6:27 PM

You might make some educated guesses, as does the guy in the 2nd post in this thread:

http://www.eng-tips.com/viewthread.cfm?qid=157377

Register to Reply Score 1 for Good Answer
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Carl_E (1); josej (2); lyn (1); nick name (1)