Battery Charger Design
12/14/2009 4:11 AM
Can you plz help me in designing of a battery charger having 5500W load .How we can select the capacity of battery set for 5 hr. back up for the above load.
Re: Battery charger
12/14/2009 4:42 AM
Is this a bettery charger, or is it really an uninterruptible power supply?
Re: Battery charger
12/14/2009 5:13 AM
how is the procedure for calculation of battery charger & battery set for a load of 5000W with 1 hr back up.
Re: Battery charger
12/14/2009 5:15 AM
Start by stating the battery voltage. Divide the Watt-hour requirement by the battery voltage to get the required battery capacity in Amp-hours, then add a bit on to that figure to cover for battery ageing and deterioration.
Re: Battery charger
12/14/2009 10:36 AM
Dear All,
1). For designing battery charger please refer to other comments.
2). Sizing battery charger as described below:
Rectifier output current = battery charging current + Design load current.
Maximum loads =P = 5000W
Design margin + Spare capacity = 5000 W x 1.2 = 6000 W
Losses = 5% (assumption value)
Total watt = 1.05 x 6000 = 6300 W.
Vdc = unknown, assumed 220 VDC (rectifier output)
Minimum output voltage 220V – 10% = 198 VDC
Maximum output voltage 220V + 10% = 242 VDC
Minimum numbers of cell = (minimum output voltage/end voltage per cell).
= 198/1.8 = 110 cells.
Based on load profile, discharge current required for 1 hour =6300/(198 x 0.9) = = 35.35A, in which 0.9 is efficiency.
Based on Voltage rating and load current we have to select the AH battery. Let say 60 AH.
A. Charging current (I charge) should not exceed than 18% of AH battery, so the charging current is :
I charge = 18% x 60 = 10.8 A
Charging rating = I load + I charge = 35.35 A + 10.8 = 46.15A
Estimated battery charger rating is 220 x 46.15 = 10,153 W = 12.69kVA.
B. Other method using floating charger for 8 hours, so the charging current is : 60 AH/8H = 7.5 A
Charging rating = I load + I charge = 35.35 A + 7.5 = 42.85A
Estimated battery charger rating is 220 x 42.85 = 9,427 W = 11.78kVA.
RSM Elect Specialist
Re: Battery charger
12/14/2009 5:22 AM
Good Answers: 42
Re: Battery charger
12/14/2009 8:31 AM
The article in the link below gives a very good idea about designing of Battery chargers. All the technical basics are available. Start designing with locally available components. Once you sget stuck up on the way ask your doubts here again.
http://www.maxim-ic.com/appnotes.cfm/an_pk/680
Good Answers: 42
Re: Battery charger
12/14/2009 8:48 AM
You may read the following link also. It will help to design.
http://cdn.vicorpower.com/documents/application_notes/an1_battery-charger.pdf