Meggering and HV DC Tests

12/16/2009 10:40 AM

Why megger is done before and after HV DC voltage withstand test

of any equipment? value of insulation resistance should increase or decrease after HV test of electrical equipment ? why ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Megger before and after HV test

12/16/2009 10:53 AM

The HV test can damage insulation, resulting in degraded isolation.

emc_c

Register to Reply
Commentator

Join Date: Sep 2009
Posts: 59
#2

Re: Meggering and HV DC Tests

12/16/2009 6:29 PM

Meggering is done once with HV. Megger testing is to catch cable that has bad insulation due to rocks in conduits, bends, or a contractor is using old old wire to deplete his inventory.

Once meggering test has passed and complete then the system is ready to go hot. I don't see a reason to megger with HV again. If that were the case there would be alot of power outtage because P&GE is meggering cable every xx months.

Meggerring resistance should always be in the giga or infinity range for good wire insulation.

It takes years for wire insulation to go bad so it does not make sense with new wire to megger after with HV.

Also there is difference between the word "Megger" and "Hi-Pot" testing. Meggering is done 480VAC or less and Hi-Pot is done on MV (12000Volts and up) cable.

Register to Reply
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#3
In reply to #2

Re: Meggering and HV DC Tests

12/17/2009 2:18 AM

Sorry rabat, I usually don't jump in or respond like this but too much of your response is incorrect for it to go without saying.

Insulation resistance testing and insulation integrity testing are both part of proper acceptance testing, troubleshooting, and long term performance documentation to aid in preventive and predictive maintenance and cost budgeting.

Once meggering test has passed and complete then the system is ready to go hot. I don't see a reason to megger with HV again. If that were the case there would be alot of power outtage because P&GE is meggering cable every xx months.

This statement just does not make good sense and at minimum it certainly implies that you need a better understanding of maintenance standards.

Meggerring resistance should always be in the giga or infinity range for good wire insulation.

Minimum insulation resistance should be approximately one Mega-ohm for each 1000 volts of operating voltage, with a minimum value of one Mega-ohm. While a higher insulation resistance is obviously better there is nothing that says only good insulation is up in the "giga range", unless it's called out in spec.

It takes years for wire insulation to go bad so it does not make sense with new wire to megger after with HV.

Please pardon my tone but this statement is just nonsense and bordering on irresponsible. I've seen cable runs that had good resistance values with a Megger and flat out fail Hi-Pot leakage tests before we get to 25%. I've seen cables that have had perfect values at startup, both high resistance and low leakage current, and 3 months later the owner is searching for the hole that popped for no apparent reason. I could go on about this one but....

Also there is difference between the word "Megger" and "Hi-Pot" testing. Meggering is done 480VAC or less and Hi-Pot is done on MV (12000Volts and up) cable.

Megger is a trademark that Biddle started and, unless they sold, AVO now owns the name as a subsidiary. A "Megger" is a layman's term for an insulation resistance tester.

Your statement of insulation resistance tests being done on 480volt or less and Hipot being done on cables 12kV and up is incorrect and is actually what prompted me to respond. That's just so wrong that at this point I'm not going to go off down that road... you should know better and if not, do some searching and find out. Go browse Megger.com and Hipotronics for a start.

My apology if I'm tired tonight and my tone is too harsh. I've just simply cleaned up too many messes and seen too many injuries because people got bad information.

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply
Member

Join Date: Jul 2007
Posts: 6
#4

Re: Meggering and HV DC Tests

12/17/2009 8:47 AM

A rule of thumb that I use is - 1 Megohm per 1000 volts plus 1 Megohm.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Meggering and HV DC Tests

12/18/2009 8:37 AM

Because during HV Test, the leakage current thro the insulation increases which might cause additional heating and subsequent de-grading of the insulation. To ensure that this has not happened, you megger after the HV Test and compare these IR values with those got before the HV Test and ensuring that the IR has not gone down drastically after the HV Test.

Register to Reply
Active Contributor

Join Date: Nov 2009
Posts: 20
#6
In reply to #5

Re: Meggering and HV DC Tests

12/18/2009 9:13 AM

Thank you very much for reply

Register to Reply
Register to Reply 6 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); cj307 (1); electricalexpert65 (1); JOSHIKD (1); rabat (1); Switchman (1)