Fire System Calculations for Commercial Buildings

12/16/2009 8:34 AM

How the calculation for ratings of fire pumps(sprinkler,jockey,main ) were done for a commercial building...any links for study materials.

What are the deciding factors for the same ???

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#1

Re: Fire System Calculations for Commercial Buildings

12/16/2009 11:03 PM

Check the local fire codes or ask the local Fire Marshall/inspector. It depends on the the size of the building, it's use, the type of construction (noncombustible material, wood frame, etc.) and several other factors.

It is not something to be guessed at.

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Fire System Calculations for Commercial Buildings

12/16/2009 11:22 PM

the respective code will describe the types of installation that is hydrant or extinguisher but always the write up if available can be help full. Please help if any body can give us a write up on the following things:-

1.types of fire hydrant

2. Hydrant calculation (like pipe dia, flow diagram,valve details),pump rating calculation

3. Water storage area calculation

best regard

Register to Reply
Member

Join Date: Sep 2009
Location: Riyadh
Posts: 5
#3
In reply to #2

Re: Fire System Calculations for Commercial Buildings

12/17/2009 12:13 AM

please follow NFPA booklet for fire standardss

Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: Aug 2007
Location: Australia
Posts: 1630
Good Answers: 20
#4

Re: Fire System Calculations for Commercial Buildings

12/17/2009 3:35 AM

I hope that you are not designing the system.

Leave it to the experts...........otherwise you may have something on your conscience that you didn't really want.............e.g. several or maybe hundreds of deaths!!!!

__________________
TO BE. or NOT TO BE. That is the question!! The Bard
Register to Reply
Participant

Join Date: Dec 2009
Posts: 2
#5
In reply to #4

Re: Fire System Calculations for Commercial Buildings

12/17/2009 5:39 AM

really i m nt a design engineer,just wanted to learn from ur comments thats y i asked that Q...

Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: Aug 2007
Location: Australia
Posts: 1630
Good Answers: 20
#6
In reply to #5

Re: Fire System Calculations for Commercial Buildings

12/17/2009 5:52 AM

That's fair enough..........just thought I would ask the question.

__________________
TO BE. or NOT TO BE. That is the question!! The Bard
Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Mar 2009
Location: Western Massachusetts
Posts: 18
Good Answers: 1
#7

Re: Fire System Calculations for Commercial Buildings

12/17/2009 12:07 PM

Based on the building construction, it's use and the contents a density in GPM/sq ft will be determined, sometimes this can be supplied by the underwriter, such as Factory Mutual or from the NFPA Codes. The second parameter to determine is the design Area to be used, this would be a typical area that will have the sprinkler heads activated when there is a fire. This also can come from NFPA or the underwriters.

This will give you the required GPM, then you have to do a flow test to determine what you can deliver to the sprinkler system. If there isn't enough pressure or capacity or both will determine if you need a Tank, Tank up in the Air, Tank with Fire Pump, etc.