Hi guys,
I am currenly in the midst of designing a system grounding for a 6.6kV 3 phase Generator.
Basically, i am just following my customer's specifications for the system grounding according to their Single Line Diagram.
They have rated their Neutral Grounding Resistor to be at 254 ohms .
If their NGR is at 254 ohms, the max ground fault current = (6600/1.73) / 254 = 15 A?
Does this mean i have to find a NGR panel with a limiting current at 15 A ?
Also, they have included a CT of rating : 50/5A 15VA 5P20.
I suppose the CT is added for the tripping of the Earth Fault Relay between the netural and the ground?
I have a Remote Control Panel For this generator also . So i suppose the Earth Fault Relay is just incorporated to send a signal back to the control panel , indicating the presence of an earth fault?
Do i need to add a neutral disconnecting switch for the grounding of this generator?
Also, in what scenario will Earth fault start to happen? ( I suppose is During Lightning and Sudden load change which will cause a sudden surge in voltage? )
Sorry for the plentiful of questions.
Would really appreciate if anyone could help me clear my doubts.