Air Conditioning at Office

12/16/2009 10:53 PM

Typically we use Air Handling Units (AHU) at large offices in India. Recently we are seeing variable Refrigerant Flow (VRF) system being aggressively promoted as something which is low-maintenance, more efficient system. We are planning a 5 floor building of 25000 Square feet each. For comfort air conditioning to our staff we need these VRF system.

I request Design experts /existing users to give their thoughts on below:

How efficient it is compared to traditional AHU (in terms of power savings for say 10000 Sq foot area)

What is its relaibility considering that in India we do not get continous power as there would be frequent failure of GRID power. During these time our stand by generator comes on.

As this is Microprocessor based system, does it possess any built-in protection against over voltage, surge, fluctuations etc.

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#1

Re: Air Conditioning at Office

12/17/2009 2:13 PM

Hello.

Direct expansion cooling systems are of course more efficient than cooling by water ones. But as refrigerant circles are more prone to failures than water circles, if in case of one VRF per one floor there is smth wrong with the central conditioner, all the floor personal suffers. If in case of one (two) water chiller(s) per the whole building smt wrong with a chiller or a system on it (which are independent), the load can be in some way economically redistributed among the left systems.

DX are greater dehumidifiers in comparison to chillers.

Register to Reply
Commentator

Join Date: Jul 2009
Posts: 63
#2

Re: Air Conditioning at Office

12/17/2009 5:04 PM

Try these,VRV or VRF, even have branches throughout India.They will have first hand knowledge of all relevant design issues/constraints etc I`m sure,together with efficiencies COP figures etc compared with more conventional systems.