Power Factor Correction

12/17/2009 12:59 AM

i have LT GENERATOR .5 M,BUT POWER FACTOR (P.F) at load .7 need design power factor correction 200kvar

ask connection power factor correction, parallel after main circuit breaker

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: power factor correction

12/17/2009 2:16 AM

This was already asked by you and answered here

Except by the last line, which does not make any sense here.

What is that you want?

1. The APFC - if you go to any site of the supplier, give the data, they will select the correct system from their product catalogue. That is a far better option than telling you the value of C (or KVAr)

2. The calculations: refer any text book. Of course we are not going to do your home work even if the question is repeated again and again

3. If you have some clarification, you should have continued on same thread. There is no point in increasing number of new threads, result will be same, or may be worse. (When one opens a thread, before answering goes through previous posts, and then answers- in a new thread there may always be a wrong answer)

Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#2

Re: Power Factor Correction

12/18/2009 11:33 AM

Mogahed,i dont really understand yr question,pls can u put it in a more understanding way(more specific),else i would just give u what i feel u may need.Also lets know yr voltage,kva or mva,kw,and yr present pf on load,is it O.7?

Awaiting yr response

__________________
Patrick Whowha
Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#3

Re: Power Factor Correction

12/19/2009 6:40 AM

Since no reply from u,kindly use the following to improve yr power factor .know yr kva,kw,frequency f,voltage E,and or yr present pf to be corrected,eg O.7.Use any of the parameters to solve yr problem,using the formulars below.

Kvar=√(kva² -kw²) using power triangle.

Q=E²/X; Kvar=E²/X; X=E²/Kvar =....Ω(capacitive reactance); Xc=1/2Πfc; C=1/2ΠfXc; C will be the value of yr capacitor to be installed in parallel to yr load.

However,yr total kvar now =inductive kvar-capacitive kvar.Your kvar must have been much more reduced.Also,yr kva will reduce to a value almost close to yr kw value,thus increasing yr pf to a higher value.This value may be up to O.95 compared to yr poor value of O.7.If u plot yr power triangle,kva and kw line will almost be close with the kvar which become very small.

If u take the steps properly,and do good calculation,u will get the right value or ratings of capacitor(in kvar and μf) to correct yr poor power factor.

Patrick Whowha

__________________
Patrick Whowha
Register to Reply Score 1 for Good Answer
Register to Reply 3 comments