12/19/2009 1:33 AM
why only third harmonics are preferred for further studies?
Good Answers: 50
Re: third Harmonic
12/19/2009 1:59 AM
Huh???
Re: third Harmonic
12/19/2009 2:35 AM
Google alternator third harmonics.
Rgards JD.
Good Answers: 50
Re: third Harmonic
12/19/2009 3:10 AM
It seems as though when an alternator is wired in a delta config with 3 phase power, the third harmonic of the sine waves can combine to create a current that flows throughout the alternator???
Re: third Harmonic
12/19/2009 3:41 AM
To add to vermins observation harmonics are fault rated at the alternator neutral star point.
Regards JD.
Good Answers: 170
Re: third Harmonic
12/19/2009 4:39 AM
Who said that only third harmonics is considered for further studies? It is not so!
However, one can say that fundamental is first order harmonics.
The second order harmonics will not have any effect as is the case with any even harmonics due to half wave symmetry.
So, the first dominant harmonics is the third harmonics. As the magnitude of a particular order harmonics is: magnitude of the fundamental / the order of the harmonics - it is easy to measure this and study further
Re: third Harmonic
12/22/2009 12:22 PM
Dear electricalexpert
I have a doubt here........3rd harmonics are zero sequence currents,so can be added arithmetically & at any instance in any phase they cancel out each other as pointed out by you in one other .2nd arder harmonics are has also no effect due to their half wave symmetry property. So both can be considered as NIL!!! then next higher order is 5th harmonics whuch has its effects on the system.(4th harmonic is again has no effects on the system)
http://cr4.globalspec.com/thread/45964#newcomments
"Know something about everything and everything about something"
Good Answers: 170
Re: third Harmonic
12/23/2009 10:34 PM
Please note that third or any triplen harmonics are added "ARITHMATICALLY" and hence would not cancel out ecah other. The resultant current of a three-phase third harmonics would be IR at an angle zero degrees PLUS IY at an angle zero degrees PLUS IB at an angle zero degrees and so they would add arithmatically (i.e.) if you have Third Harmonic IR 3A and so also IY & IB, the resultant Thgird Harmonic Currremt would be 9A and it would accumulate in the neutral. Only vector sum of balanced currents would be zero and not the arithmatical sum.
Re: third Harmonic
12/31/2009 2:21 AM
How can we prevent the destructive effect of Harmonics in computer system and UPS system connected to generator system?
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member
Re: third Harmonic
03/13/2011 1:20 AM
nice info
One system