12/22/2009 11:20 AM
I have an old KW meter (4 dials on face 0-9) used for residential 240 volt AC service.
This old meter was of about 1950 vintage the type you would see on a pole in the alley behind your house.
I am connecting it to a tank heater that is only 120 VAC to measure the KW usage. My question is, the KW meter is 240 VAC and I am running only 120VAC through it will the reading be correct?
Does this meter measure watts or amps and calculate the watts? If it measures watts I believe it to be accurate with 120VAC. If a calculation is done from amps (current draw) then the KW usage would be double the reading.
Mac
Re: KW usage for horse take
12/22/2009 12:34 PM
What you have is a watt hour meter. You can find out everything you need by clicking.
Re: KW Usage for Horse Take
12/22/2009 11:47 PM
That meter is 240 V with a neutral ( the neutral is connected to ground inside the dwelling) the two power leads go the fuse/circuit breaker panel. If in the dwelling you some how only used 120v on one leg of the incoming power the meter would of course still read the KW properly. So I do not see a problem with reading watts into a heater. Of course you could posibly split the heater elements int two different 120 v legs and then balance thru the meter
Bin there, done that, then done that again and again and now I forgot where I was.Is this what it means to get old?
12/23/2009 8:43 AM
New electric meters for the most part would not register any kWh unless you have a 240 supply to them. The load can be 120 as long as the supply is 240. With a meter that old, it should work just fine on 120 volts only and will probably be as accurate as you would need. Calibration might be off slightly but the difference won't be much. As was mentioned earlier in another posting, this meter measures kWh. It reads kWh, not amps.
12/23/2009 9:01 AM
Thanks, I have the info I needed. Happy Holidays
Mac
Good Answers: 151
12/23/2009 10:26 AM
I am assuming that you are in North America and have 240 V, 3 wire service. (240VAC in Europe and European meters are different animals). If the meter is rated for 240V it means that it has a 240V potential coil and this coil must be wired to 240V for the meter to be at all accurate. If this is the case, than loading either 120 V leg will give you an accurate reading of Watt-Hours. If you only have 120V service than you need to find a meter with a 120V potential coil.