12/24/2009 12:38 AM
Dear Friends,
I have an old DC drive for 94KW for which I want to configure if it is a single quadrant drive or four quadrants? The drive has 6 thyrister modules and four control wires are coming out from each module. It seams like each module contains two thyristers and thus a 4 quadrants drive. Is there any other check list for which I can configure the drive? Actually I don't have sufficient experience with DC drives.
Good Answers: 80
Re: How to configure the drive is 4 quadrants?
12/26/2009 12:47 PM
The answer is NO you cannot make a real four quadrants drive with this.
A typical four quadrants drive would use 12 thyristors. It is basically two full bridges in opposite polarity. The two independent firing modules must be tightly controlled at the point where the current reverse from one bridge to the other.
But...
What you could do is use a reversing contactor to get a slow reversal when needed. The drive controls would probably need to be modified but it would work in a slower fashion.
01/01/2010 4:26 AM
Thanks,
It means if a drive has 12 thyristers, it is 4 quadrant while if a drive has 6 thyristers, it is single quandrant.
Am I right?
Sory for my lack of basic knowledge.