Previous in Forum: SOV Valve   Next in Forum: Pressure Control Valve Parallel Operation
PCV:Why Pressure Control Valve are Connected in Parallel
12/24/2009 2:20 AM
Hello guys,
i wana know why pressure control valves are connected in parallel for the inlet of veritcal vessel,during the HAZOP of this section there were a debate on the issue but due to lack of control phlosophy it was a little difficult to get clear answer.
jsut i wana any one explain what might be the possible reason,i blieve we are going to alocate the document for the cause,but i need to have some knowldge on the subject.
thank you
Re: PCV:WHY PRESSURE CONTROL VALVE ARE CONNECTED IN PARALLEL
12/24/2009 3:24 AM
The usual reason for such a scheme is that one valve will not fill or pressurize the vessel fast enough during high-flow demands, so you add a second valve. The control system can activate neither, one, the other, or both valves.
United States - Member - US Citizen - Born & Raised Engineering Fields - Control Engineering - HVAC/R Simplified Using PLC Controls Engineering Fields - Instrumentation Engineering - HVAC/R Simplified Using PLC Controls Engineering Fields - Energy Engineering - HVAC/R Simplified Using PLC Controls
Re: PCV:Why Pressure Control Valve are Connected in Parallel
12/24/2009 11:09 PM
Not quite sure if I understand your operation.
If you are using a 1/3 - 2/3 valve arrangement in parallel, the reason is to keep the valve seats from wire drawing when the capacity requirement closes the valve to near 0%. The theory requires the 1/3 valve to open fully and then have the 2/3 valve open for additional capacity. Some programmers open the 1/3 valve fully and when additional capacity is required, they close the 1/3 valve and modulate the 2/3 valve. The point is to keep whichever valve is operating at mid-span or higher to prevent wire drawing.
"Memorize the calculations, you look like a fool searching your notes while teaching class"