Calculating Interrupt Cycles

12/29/2009 8:59 AM

hello friends......

how to calculate interrupt cycle (fault duty).....in dubai faulty duty for

main distribution board is = 50ka and sometime 65ka.

sub main distribution board = 35 ka

distribution board = 25 ka

above said are usually implemented.but however i request you to please expalin me isit calculated from below factors?

1.total load?

2.cable size?

3.maximum demand?

4.main incomer ratings in amps?

i need a clear answer even on what factors fault duty in panel boards depends and what factors whould be taken in consideration on calculating fault duty...........?

thanking you..................

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Calculating Interrupt Cycles

12/29/2009 6:21 PM

The utility provides the available fault current at the service point on the building. It will vary depending on the utility system. You then must choose equipment that will match this fault current. For the sub panels, you must calculate the fault current for each panel using the fault current at the main panel as the source.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Dec 2009
Location: Jakarta 12130 Indonesia
Posts: 76
Good Answers: 1
#2

Re: Calculating Interrupt Cycles

12/31/2009 3:33 AM

Dear Sir,

Fault duty i.e. 50 kA, 65 kA, 35 kA and 25 kA are symmetrical fault current issued by switchgear manufacturer that their equipment already passed the test (type test) by independent laboratory and able to withstand against fault on those values (maximum).

During equipment sizing we conduct a short-circuit study. Simple system may be calculated by hand, but for complicated system which are consist several bus sometimes more the 100 buses we have to calculate by using software i.e. ETAP, EDSA, and etc.

Prior to conduct calculation we have to provide single line diagram of impedance, which consist of:

1). Current sources such as: Synchronous generators, synchronous motor or condensers if any, induction machine (motor and generators), electric utility system if any and adjustable speed induction or DC motors.

2). Single line diagram indicate the impedance of current sources, cables, transformer and motors.

3). To determine the operation scenarios for normal operation and abnormal condition (the worst operating scenarios).

4). To operate with minimum and maximum generation (Numbers generator required).

5). To recognize and implement subtransient reactance (determine current during first cycle after fault occurs) and transient reactance (to determine current after several cycles).

The calculation result on each bus shall be less than kA switchgear, let say. We selected 31.5 kA if the calculation result is less than 31.5 kA. Some company stated that the calculation results shall be 31.5 kA – 10% x 31.5 kA = 25.2 kA, other company takes 5% only.

If the calculation results slightly higher than 31.5 kA, we have to select switchgear 45 kA (if any).

If you want more clear about s.c calculation please read IEEE-Std 141-1993, Chapter.4.

Regards,

__________________
RSM Elect Specialist