Generator Excitation

01/05/2010 7:55 AM

Why is the excitation of a generator (not a generator transformer unit) switched ON at near to rated speed?

For example, the excitation of 750rpm rated speed generator is switched ON at 560rpm. Switching ON of the excitation a very low speed would have overloaded the excitation system and the V/f ratio would have increased leading to overfluxing. If thats the case, the excitation should have been switched ON at rated speed. But it is usually done at near to rated speed. Why?

Register to Reply
Pathfinder Tags: Generator Excitation
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: Aug 2008
Location: TN, India.
Posts: 35
Good Answers: 2
#1

Re: Generator Excitation

01/05/2010 9:44 AM

Excitation is switched at near to rated speed only as it gives the indication of incoming voltage at the acceleration stage itself and that is to be matched with the running voltage for synchronizing.

But in your case 560 rpm is not near to 750 rpm. So I dont know the reason for your session.

__________________
?????????? ????????? ????????,.........??????? ???????????? ???????? ????. ????????????
Register to Reply
Associate

Join Date: Sep 2009
Location: Singapore
Posts: 28
#2

Re: Generator Excitation

01/05/2010 8:40 PM

Excitation at low speed builds up some voltage required

However, Overexcitation will only cause generator to perform at lagging PF, underexcite will cause the generator to perfom at leading PF.

Register to Reply
Commentator

Join Date: Dec 2009
Location: Mangalore, India
Posts: 65
Good Answers: 4
#3
In reply to #2

Re: Generator Excitation

01/05/2010 11:33 PM

Lagging or leading ower factor operation of the generator comes into picture when the m/c is loaded. But why should be the excitation switched ON at near to rated speed only?

Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#5
In reply to #3

Re: Generator Excitation

01/06/2010 3:17 AM

ok Sir... Let me go back to the fundamentals... The Induce emf in alternator depends on the speed of the rotor, and the excitation current. suppose if the speed of the rotor is brought upto synchronous speed or near Ns.. and then we turn on the full excitation. would'nt the flux linkages with stator windings be better and hence the induced emf..

Register to Reply
Active Contributor

Join Date: Jul 2008
Location: Mombasa, Kenya
Posts: 24
Good Answers: 1
#4

Re: Generator Excitation

01/06/2010 2:54 AM

You are right about overfluxing at low speeds. Most Automatic voltage regulators I know have a function called Under-frequency Roll-off. The point at which the AVR goes off on the speed curve during shut-down is the same as that at which it comes on during start-up. This is to allow the terminal voltage to decay fast enough during shutdowns (safety feature). Usually this is 80% of rated speed.

Secondly, consider cases where a load has not been isolated during start-up. What would happen if the voltage was to build up together with speed? During start-up the electromagnetic processes in the generator are in a highly dynamic state and may either collapse or lead to overshooting desired values. That is a calculation I am not willing to delve into. I think the important thing is during shut-down, terminal voltage has to decay at a fast rate. The relay to switch on/ off is one and has that one setting.

__________________
Curiosity has its reasons for existence - Albert Einstein
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#6

Re: Generator Excitation

01/06/2010 7:36 AM

Though the exitation due to residual mag is there to develope some voltage for controls but not for load which should only be switched on when the Frequency is in the region where system can capture to synch to the specified frequency*** i.e. 50 /60 Hz. In your case it may be due to the manufacturers' option for any reason you should look into.

*** The Gen-sets being used on power-net need to be synchronised with main source.

.

Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#7

Re: Generator Excitation

01/07/2010 10:23 AM

560rpm is not near to 750rpm to be accepted as near to rated speed.Lets say for example, 730rpm or 740rpm can be said to be near to rated speed of 750rpm.

When generators are excited,it is to start the gen at its rated speed,but when it is loaded,the speed drops slightly within tolerance range.The generator should run on no-load or close to rated speed,so that it maintains its rated voltage output within tolerance as well as its frequency when loads are switched on.Some load may drop the voltage so low to affect other loads as well as the gen set.

Pls read further on generator excitation.

Patrick Whowha

__________________
Patrick Whowha
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers: