Cable Lug Diameter

01/05/2010 7:45 AM

Why is the lug inner diameter more than the cable core diameter?

I have a 500sq.mm single core stranded aluminium cable whose core diameter is 26.4sq.mm. Corresponding copper lug inner diameter is 30mm. Ofcourse, the cable inner diameter should be slightly more than cable core diameter so that the lug easily slides along the core; also, the difference between the lug ID and the corresponding cable core diameter increases in proportion to the cable core diameter. Why?

Register to Reply
Pathfinder Tags: Cable lug
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Cable Lug Diameter

01/05/2010 3:09 PM

I think the lug you have is for stranded copper wire.

the extra space is for the gap around the strands.

Can you use a copper lug on a aluminium wire?

Register to Reply
Commentator

Join Date: Dec 2009
Location: Mangalore, India
Posts: 65
Good Answers: 4
#2
In reply to #1

Re: Cable Lug Diameter

01/05/2010 11:30 PM

Ofcourse, you can use a copper lug for aluminium cable but the opposite should not be done. Cable of larger cross sectional area usually use stranded conductors for better tensile strength. However, Im not clear as to why the lug ID is considerably more than the corresponding cable core diameer.

Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#3
In reply to #2

Re: Cable Lug Diameter

01/06/2010 11:50 AM

You are correct in regard to copper lugs on aluminum cable and that the reverse is not recommended. However, in that application the copper lug should be tinned or otherwise plated and a contact aid or sealant, typically containing grit, should also be used to seal the connection. The aluminum strands should be carefully and thoroughly cleaned to remove the non-conductive aluminum oxides before making the connection. (Aluminum rapidly oxidizes on exposure to air). The aluminum strands are normally wire brushed with a SST wire brush in air, wiped with a clean cloth or wiper then a thin coat of contact aid is applied and the surfaces wire brushed again through the contact aid to trap any remaining oxides. Wipe the excess and make the compression.

You don't indicated the stranding but, based on your description, it may not be standard concentric stranded AAC conductor but compression lugs and conductors are matched to the recommended compression dies or tool to achieve specific area reduction ratios.

I will take exception to your reasoning for cables of larger cross sectional area and diameter being stranded for better tensile strength. That's not the reason at all. They are stranded for economy, efficiency and flexibility. Stranded all aluminum conductors will have lower tensile strength than a solid all aluminum conductor of the same cross sectional area. That's also reflected in ASTM standard stranding strength reduction factors. The reason, of course, is that in order to achieve full tensile strength, the strands have to be near-uniformly loaded and that's difficult to achieve when compressive load is transferred to and perhaps through the strands (depending on the number of strand layers). ASCR and other conductors with high strength cores achieve full tensile strength because the core is gripped separately from the outer strands.