Loss of PROFIBUS Communication

01/05/2010 3:27 PM

I have a single frequency convertor( FC) connected in the middle of a profibus network. Been working correctly for 6 months. Has failed with loss of communication. Replaced FC 3 times proved FC removed are good. Profitrace shows bus voltage to this address is good . DCS shows intermitant fault word dropping the communication, but fault is not there long enough to be permanent. All connections in the loop are tight. Have proved the software is good. Have replaced the hub the loop is supplied from. Fault can be cleared by running a seperate profibus cable from a different hub to the FC. If this cable is connected to the orginal hub the fault reappears. There is no double address. unable to find any shorts in the loop to the screen. Any additional suggestion of where to look will be most useful.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Apr 2008
Posts: 20
#1

Re: Loss of PROFIBUS Communication

01/06/2010 12:31 AM

Is one of the small wires touching another on the connector of the profibus or is one of the wires held to the connector with one strand.

Register to Reply
Anonymous Poster
#5
In reply to #1

Re: Loss of PROFIBUS Communication

01/06/2010 4:33 PM

Solid strand of cable.

Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#2

Re: Loss of PROFIBUS Communication

01/06/2010 4:11 AM

Hi there,

I have had a similar problem to this before.

You should check that your screens on the PB cable are continuous and that they are all on the same earthing point. It could be that your older hub earthing point is different to that of the FC. This would cause huge interferences with the communications.

If you are lucky enough to have a decent oscilloscope then download the Profibus installation guides from www.profibus.com/downloads They have a fault finding section that will explain to you what the trace that you will see on the scope means. They will also give you a good few guidelines about the installation that might reveal your problem.

All in all - good luck and please keep us posted?

Regards,

Craig

Register to Reply
Anonymous Poster
#4
In reply to #2

Re: Loss of PROFIBUS Communication

01/06/2010 4:31 PM

Have looked at the earthing. This appears to be ok. The FC is mounted next to 5 others but they are on a different loop. I dont think there will be a quick fix to this problem.

Register to Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#3

Re: Loss of PROFIBUS Communication

01/06/2010 4:20 AM

Have you been able to look at the signal levels? FC are 'noisy' devices so there may be a possibility that this is coupled to the PB lines at this point swamping the signal. The fact it works with no other connections and less cable may reinforce this idea. Does this happen when FC is not running too (just SMPSnoise then) and can you power the control and no main power to test. If so, use a lower control voltage which would also reduce noise levels. What has the FC supplier suggested? If nothing else, I would try connecting a small filter capacitor (0.1μF) from the FC Ov connections (there may be two, analogue and digital) to ground which may help.