I have a single frequency convertor( FC) connected in the middle of a profibus network. Been working correctly for 6 months. Has failed with loss of communication. Replaced FC 3 times proved FC removed are good. Profitrace shows bus voltage to this address is good . DCS shows intermitant fault word dropping the communication, but fault is not there long enough to be permanent. All connections in the loop are tight. Have proved the software is good. Have replaced the hub the loop is supplied from. Fault can be cleared by running a seperate profibus cable from a different hub to the FC. If this cable is connected to the orginal hub the fault reappears. There is no double address. unable to find any shorts in the loop to the screen. Any additional suggestion of where to look will be most useful.