We are commisioning an old avr model siemens thripart bp92 110345.We donot have manual for this avr. After installation and starting engine, voltage built up but after synchronization we could not control pf and generator undereactance relay operated. Does someone has solution or some tip for this problem.
Re: Siemens Thyripart AVR
02/11/2010 1:21 PM
hi,
There should be big resistor is also readjustable.
readjust setting for this one, will readjust droop voltage
good luck
freerk
05/04/2012 8:23 AM
Dear Siemens owner
in regards to your generator matters with THYRIPART excitation support, please email me one page drawing with model and serial number of subject generator (if no drawings available send me couple photos showing the excitation system)
As a reminder, Siemens generators are compounding excitation with inverse regulation, THE AVR dose not provde excitation The AVR is to supress OVER EXCITATION during load conditions, Droop transformer must be in correct phase in order to function properly,