Why Neutral size is 200% of the Phase for UPS distribution?

01/09/2010 9:59 AM

All the U.P.S distribution panels are being provided with busbars of TP+2N ie., the neutral size is 200% of the phase busbar. Why?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Why Neutral size is 200% of the Phase for UPS distribution?

01/09/2010 5:30 PM

The designer must think there will be a harmonic problem.

Reply Score 1 for Good Answer
3
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Why Neutral size is 200% of the Phase for UPS distribution?

01/09/2010 7:05 PM

What does TP+2N mean? Is the UPS output single phase 3 wire (2 Line, 1 Neutral) or three phase 4 wire (3 phase 1 Neutral)?

If it is three phase 4 wire system, then wareagle's answer is correct in the consideration that the UPS loads are non-linear which generates harmonic currents. For non-linear loads, the return currents from each of the three phases are in phase in the neutral path for 3rd harmonic current and so the total 3rd harmonic neutral current is the arithmetic sum of the three individual 3rd harmonic phase currents. This is also true for odd multiples of the 3rd harmonic (9th, 15th, 21st, etc.). Generally, a neutral conductor is sized for 150 percent of the phase current in this case. I would like you to see the previous posting http://cr4.globalspec.com/thread/43708 for details.

Otherwise, the answer may different. In this case, most probably the neutral is designed to carry the return current of the sum of the both lines.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 3)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Why Neutral size is 200% of the Phase for UPS distribution?

01/09/2010 9:29 PM

To size the neutral to take care of the accumulation of Triplen Harmonic Currents, which are quite normal in any UPS.

Reply
Reply to Forum Thread 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); msamad (1); wareagle (1)