Could someone there advice: I have just rewired a residential house and inorder to control overcurrent and earth leakages, I installed all the circuits with Rcbos. And because the type of earthing used is a TT system, I have installed a RCD and MCB at the incoming mains. Now the querry is when I reset the Main RCD, either all the Rcbos trip or the RCD trips. But when I bypass the RCD, the Rcbos operate well. So could this mean that the problem is with the incoming mains?

How can I find out?

__________________
"It doesn`t make sense to hire smart people and then tell them what to do, hire smart people so they can tell you what to do."--- Steve jobs.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#1

Re: Member

01/09/2010 2:50 PM

WTH is the BFD? Your communication is NFG. Have you considered a GF?

Register to Reply Score 2 for Off Topic
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2
In reply to #1

Re: Member

01/09/2010 8:12 PM

Don't be so narrow minded. All of the acronyms he used are legitimate for countries other than the US. Just because they mean nothing to you doesn't mean you should mock him.

RCBO = Residual Current Circuit Breaker with Overcurrent Protection: this is essentially the same as a Ground Fault Circuit Breaker. Residual Current is a form of Ground Faul detection, as opposed to Zero Sequence. Here in the US we don't use ZSGFP unless you have a resistance grounded system, which is never the case in residential applications, so we don't bother with the distinction and call everything "Ground Fault".

TT system; In other countries, they have a nicely defined way of describing the way their power delivery is connected to earth (ground), spelled out in International standard IEC 60364 as three families of earthing arrangements, using the two-letter codes TN, TT, and IT.

The first letter indicates the connection between earth and the power-supply equipment (generator or transformer):

T

:direct connection of a point with earth (Latin: terra);

I

:no point is connected with earth (isolation), except perhaps via a high impedance. Here in the US we would call this an Isolated Ground system (IG), as typically seen in hospitals where sensitive medical equipment is going to be plugged in.

The second letter indicates the connection between earth and the electrical device being supplied:

T

:direct connection of a point with earth

N

:direct connection to neutral at the origin of installation, which is connected to the earth. They need to differentiate here because unlike the US where all residences use Line and Neutral for powering devices, in other countries they do not.

RCD = Residual Current Device; This is a Ground Fault device that is external to a circuit breaker, in other words, like a GFCI receptacle, except wired to the circuit breaker to trip it (using a Shunt Trip).

MCB = Miniature Circuit Breaker. These are essentially the equivalent of our residential circuit breakers, as opposed to MCCBs, which are Molded Case Circuit Breakers, although here in the US, residential CBs are still Molded Case.

OK, class dismissed.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#6
In reply to #2

Re: Member

01/11/2010 3:00 PM

JReaf,

You said it right. These are commonly used so most of us understand it.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Member

01/10/2010 4:31 AM

Isolate the house from the mains and start measuring for ohms between neutral and earth on each of the RCBO circuits; they should all present v.high resistance. One that isn't indicates a fault that needs to be rectified before the installation will work properly.

Check that all of the RCBO circuits' neutral conductors are wired downstream of each RCBO and not connected inadvertently directly to the common neutral bar upstream of them.

After that, report back here with the findings. <Subscribes to discussion>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Active Contributor
Safety - Hazmat - New Member Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Dec 2009
Location: Kampala
Posts: 24
#4
In reply to #3

Re: Member

01/10/2010 8:33 AM

Thanks Pwslack, for the suggestions. Actually the type of Rcbos I used are the Merlin Gerin C60H. And I made sure that the Blue/neutral supply lead from the Rcbo is connected to the neutral terminal block and load neutral is connected to the out going terminal of the Rcbo.

__________________
"It doesn`t make sense to hire smart people and then tell them what to do, hire smart people so they can tell you what to do."--- Steve jobs.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Member

01/11/2010 3:29 AM

OK.

And the circuit neutral-to-earth resistance values?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ace Boeringa (1); JRaef (1); luyombya (1); PWSlack (2); V.I.Abraham (1)