Motor is 3300KW @ 6.6kV
I know this does not make sense but :
Motor does not run up but reported to behave as though single or 2 phasing
Switchboard voltage drops by around 500V, even when motor was started uncoupled from its pump
Motor PI, IR & winding balance tests all ok
VCB tested - IR ( open & closed ) & Ductor checks ( closed ) all ok
Cable IR tested & even energised from breaker for 30 secs ( motor ends disconnected ) to eliminate switchgear surge arrestor problems.
Differential CTs in motor seem ok
The motor is Star / Star windings in parallel - windings tested seperated - all balance ok
Tan / Delta testing of motor windings shows no areas of concern
The motor protection relay has been secondary injection tested to prove short circuit, overload, earth fault & out of balance functions
We intend to Baker test next to detect shorted stator turns ?
Please note the Motor does not trip on protection !
It pulls normal starting current - around 1600 amps.
The board incomer feeder relay does not help us from its event log.
You will appreciate we are reluctant to attempt to start the drive again until we find the cause of the problem - to be honest, if it were not for us witnessing the motor not accellerating, it would feel like we were trying to find a fault we knew were not there !
We are preparing to install a data logger on the board bus wired VT volts & the circuit phase CT secondary's - for when we next run the drive.
This drive is part of a turn key project - just handed over to us, & is a warranty issue if we find a fault, but difficult to initiate with no evidence of a fault.
We have almost exhausted ideas for fault finding investigation.
Other discussions have included possible supply transformer saturation, broken rotor bars or end rings on the motor, plus many more.
Can anyone offer advice or ideas for further testing on this HV motor ?
Has anyone seen this kind of thing before, where a fault has been hidden somehow ?
Any advice or ideas greatfully received,
CTB