for a constant range of cooling tower/condenser, hvac make up water & condenser water flow rate demand depend upon compressor power kw/ton as compressor power decreses respectively demand decreses what type of compressor we should select for economical design

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#1

Re: HVAC MAKE UP WATER & condenser water flow rate SAVING

01/12/2010 2:20 AM

manis2k3; how about a valve that changes flow with head pressure or a variable speed compressor. perry

Register to Reply
Associate

Join Date: Jan 2010
Posts: 28
#2
In reply to #1

Re: HVAC MAKE UP WATER & condenser water flow rate SAVING

01/12/2010 6:39 AM

dear sir i m agree with ur suggestion of variable compressor bcoz due to variable heat load, there will be need of a compressor with VFD Control but i m talking about specific power consumption (kw/ton) of compressor. type of compressor (reciprocationg/screw/centrifugal) and which is the best for economical and good design

Register to Reply
Associate

Join Date: Jun 2008
Posts: 25
#3

Re: HVAC Make Up Water & Condenser Water Flow Rate Saving

01/12/2010 8:43 AM

You can use screw compressor.

Register to Reply
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#4

Re: HVAC Makeup Water and Condenser Water Flow Rate Savings

01/13/2010 4:53 PM

It depends on the application such as low temp, high temp or AC, etc. You need to know what the maximum and minimum loads will be. Some compressor designs are better than others for a set application.

Your other main concern will be oil return to the compressor at low demand. The whole system has to be designed with this in mind.

Your compressor options are: rotary, scroll, screw, reciprocating, centrifugal, variable speed, multi speed, multi stage parallel or a combination of the above.

Register to Reply
Anonymous Poster
#5

Re: HVAC Makeup Water and Condenser Water Flow Rate Savings

01/16/2010 4:43 AM

Foy your info, please see recommended items for your review and consideration;

1. Chiller selection:

a. Trane CTV chiller (R123 refrigerant) rated effeciency from 0.45Kw/ton to 0.52 at 87F condenser temp

b. York CTV chilller (R134a refrigerant) rated effeciency from 0.58kw/ton and higher

c. Mcquay chiller(R134a refrigerant) rared effeciency from 0.742 kw/ton and higher -

d. Screw chilller are rated above 0.80kw/ton

e. Receprocating compressor are rated above 1.2KW/ton

2. Other areas that need to achieve subtantial savings are pumps size selection, VFD application consideration and Cooling tower application and optimization.

Nelson

Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Icarus (1); manis2k3_knit (1); perry (1); takle (1)

Previous in Forum: Gear Box Spares for Eicher Tractor, NC 234   Next in Forum: headloss in bypass control valve in hvac
You might be interested in: Compressor Repair Services, HVAC Chillers, Condensers

Advertisement