Differential Pressure Flow Switch Across a Pump

01/12/2010 9:40 AM

I have a Pump For the LTHW system of a building I am currently working at I have found that the Flow Switch across this has stopped functioning.

It had a Range of 0.5 – 11bar

the pump is a

Grundfos Unit

Type NK125-400/415BAQE

Model K78111L4-20290/2-3063

Q 356.4 m3/h H 49.46m

P/t10/120 bar/c max

and the system runs at about 160KPa line pressure

we couldn't find a like for like replacement but the supplier came back to me with an option for a .5 - 4bar unit that is the same physically and I think should work.

First and main question is this going to work ?? everything else is only for my own amusement.......

secondly how would I calculate this or is there a guide I can use? the simpler the better.

Should I be able to determine this from looking at the label ?

I can't locate the pump on the Grundfos site :( I might be looking in the wrong area not sure.....

any help will be muchly appreciated

__________________
lost.instro
Register to Reply
Pathfinder Tags: Pump Differential pressure
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant
Engineering Fields - Manufacturing Engineering - New Member

Join Date: Jun 2008
Location: Tulsa, OK
Posts: 2
#1

Re: Differential Pressure Flow Switch across a pump

01/12/2010 10:23 AM

What is the intended control function of this flow switch?

Register to Reply
Active Contributor

Join Date: Sep 2008
Location: Mount Isa
Posts: 22
#2
In reply to #1

Re: Differential Pressure Flow Switch across a pump

01/12/2010 10:29 AM

Purely for indication of flow to prevent dry running and if the pump fails to let the BMS know so it can start the pump changeover sequence

__________________
lost.instro
Register to Reply
Participant
Engineering Fields - Manufacturing Engineering - New Member

Join Date: Jun 2008
Location: Tulsa, OK
Posts: 2
#5
In reply to #2

Re: Differential Pressure Flow Switch across a pump

01/12/2010 10:49 AM

The flow switch should work OK. I would only verify that the output is readable by whatever device is controlling the shutoff switch. Typical LTHW system operate at a max pressure of something like 2-3 bar at most. I'm curios as of why the original switch went all the way up to 11 bar.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#3

Re: Differential Pressure Flow Switch across a pump

01/12/2010 10:35 AM

Should work fine (160 kPa = 1.6 bar).

What's the switch for?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Active Contributor

Join Date: Sep 2008
Location: Mount Isa
Posts: 22
#4
In reply to #3

Re: Differential Pressure Flow Switch across a pump

01/12/2010 10:39 AM

Flow indication if the pumps running.....

I thought the same but what will be the pressure on the other side of the pump I have indication from the BMS that the pipe work is 1.6bar on the flow side, can we assume there will be a vacuum pulled or negative pressure on the other ???

__________________
lost.instro
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #4

Re: Differential Pressure Flow Switch across a pump

01/12/2010 10:52 AM

<...there will be a vacuum pulled or negative pressure on the other ???...>

It depends upon a criterion known as the Net Positive Suction Head [NPSH] of the system. It needs local assessment, as it cannot be seen from here. Too hard a suck from the pump causes cavitation, a fluid/system phenomenon capable of wrecking a pump in short order.

Make sure that the replacement sensor, whatever its selected range, can withstand the maximum system pressure downstream of the pump. This pressure is the sum of:

  • the pump-only closed-delivery-valve pressure (which can be found in the pump manufacturer's performance information sheet) and
  • the upstream pressure at the pump suction connection.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#7

Re: Differential Pressure Flow Switch Across a Pump

01/12/2010 1:03 PM

Cheers for that I am now pretty confident that it should be ok

Line pressure is well under the rating of the Sensor I was just worried that it wouldn't switch and indicate flow..... very embarrassing

Register to Reply
Member

Join Date: Dec 2009
Location: Moscow, Russia
Posts: 8
#8
In reply to #7

Re: Differential Pressure Flow Switch Across a Pump

01/13/2010 6:12 AM

You could go for a thermo mass technology instead of a DP. There's a number of manufacturers making thermo mass flow switches. I suggest you pick one which is able to perform flowmeter function with 4-20 mA output being a SSR relay device (switch) indeed (I'd look at http://kayden.com/). Thus, one gauge would meet both of your targets and eliminate tentative headake with impulse line clogging (if any), process fluid density changes, leaks etc.

I'd pay atention for pressure limits while selecting thermo mass switch, despite it would install upstream of the pump normally.

RS-485 Modbus communication might be of help as well.

Juri.

Register to Reply
Active Contributor

Join Date: Sep 2008
Location: Mount Isa
Posts: 22
#9
In reply to #8

Re: Differential Pressure Flow Switch Across a Pump

01/13/2010 9:47 AM

Thanks for the input but way over complicated and I can imagine that a thermo mass flow switch with mod bus would be buckets of cash more then the £113 we are forking out..... keep it simple like for like this one has lasted 7 years so its not like a repeat problem......

__________________
lost.instro
Register to Reply
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#10
In reply to #9

Re: Differential Pressure Flow Switch Across a Pump

01/13/2010 5:05 PM

If there are two small diameter tubes running to the switch; one from either side of the pump than I would check to see if they are clear, especially if the tubes are a dissimilar metal from where they are attached. Plugged tubes will mimic a failed switch.

Register to Reply
Active Contributor

Join Date: Sep 2008
Location: Mount Isa
Posts: 22
#11
In reply to #10

Re: Differential Pressure Flow Switch Across a Pump

01/14/2010 1:43 AM

yeah the impulse lines are cleared, we ran water out of both sides the diaphragm seems to be all gunked up or maybe the spring ???

you can get the contact to close if you push really!!!! hard on it from both side but the pump doesn't have enough pressure to make it close, could possibly rebuild it but better to have a functioning unit, then one that is likely to seize up again ........

__________________
lost.instro
Register to Reply
Member

Join Date: Dec 2009
Location: Moscow, Russia
Posts: 8
#12
In reply to #11

Re: Differential Pressure Flow Switch Across a Pump

01/14/2010 6:32 PM

If your loop is critical, you should think of redundancy or better technology. DP switch with its diaphragm and mechanical moving parts is being weared out by your process in a very agressive manner, you may not see it - vacuum issues, sticky dirt and sediment layer impact on diaphragm, vibration/cavitation, impulse line clogging etc. 133 GBP are peanuts compare to pump repair costs or its replacement. Also, count for losses if your process is down because of that pump failure. Third is a headake of your own to handle all that stupid work. However, building HVAC systems are not critical for people to survive as in general. Just chill them down a bit .

In case of thermo mass technology the dirt sticking is questionable, as the switch heats up the sensor and process fluid velocity helps to keep the sensor clean. The company I pointed out makes 3 types of switches and the cheapest one is some 300 USD List, while you always have to pay extra for things like advanced communcation etc (and save on cabling again). There's nothing to wear, non-coating, adds a flow rate across your pump. I would try to weigh all above up and note down "+" and "-"

Register to Reply