Cable Hipot Before Megger or Megger Before Hipot?

01/14/2010 2:25 AM

Hi:

Would you please answer the following questions?

Should the AC Hipot test be done before the Megger testing? Or should the Megger test be done before the AC Hipot? Or it does not matter.

Would applying one before the other cause damage to the cable?

The protective device for an old calbe rated at 69kV with three splices had just tripped off on ground and it would be necessary to test the cable.

If the questions were answered previously, I apologize for this posting.

Enjoy your time by helping others

Register to Reply
Pathfinder Tags: cable testing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Cable Hipot before Megger or Megger before Hipot

01/14/2010 6:42 AM

Hipot first. The stress of the test can damage insulation - the Megger test will catch it.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Cable Hipot Before Megger or Megger Before Hipot

01/14/2010 8:18 AM

Usually, IR values are taken both before and after the Hi-Pot Test and the IR values are compared to see if there had been any damage to the insulation on the application of the high test voltage.

Register to Reply Good Answer (Score 2)
Participant

Join Date: Jan 2010
Posts: 3
#3
In reply to #2

Re: Cable Hipot Before Megger or Megger Before Hipot

01/14/2010 3:39 PM

Thank you both;

The normal Megger test is about 5 or 10 kV DC, would applying this voltage cause a damage to the cable or detect the fault on aged cables? In the post case, the megger test did not detect a fault since it is below the service voltage of the cable, although it is DC.

Enjoy helping others

Register to Reply
Active Contributor

Join Date: Nov 2009
Posts: 14
#4
In reply to #3

Re: Cable Hipot Before Megger or Megger Before Hipot

01/15/2010 5:14 AM

why not PD test - it will help you to locate problem when megger just confirm tt IR is not well.

Register to Reply
Anonymous Poster
#5
In reply to #3

Re: Cable Hipot Before Megger or Megger Before Hipot

01/15/2010 5:59 AM

True! An IR Test may not damage the cable insulation as the test voltage is less than the rated voltage of the cable. But, the Hi-Pot test voltage is definitely much more than the rated voltage of the cable. (To be exact, 125% to 150% of the rated cable voltage will be the AC Hi-Pot Test Voltage and the DC Hi-Pot test voltage will be 1.7 times the AC Test Value). So, there is a possibility that this high voltage will definitely cause damage the cable insulation, particularly, if the insulation is already weak.

Register to Reply
Power-User

Join Date: Apr 2009
Location: FL USA
Posts: 372
Good Answers: 9
#6

Re: Cable Hipot Before Megger or Megger Before Hipot?

01/15/2010 8:15 AM

Seems like the best approach is to follow electricalexpert65's good advice and limit the applied voltage to whatever margin (10%?) above cable rating you would expect the cable to experience in your planned application.

__________________
What is right is not always popular. - What is popular is not always right.
Register to Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#7

Re: Cable Hipot Before Megger or Megger Before Hipot?

01/15/2010 9:17 AM

Sometimes testing only confirms our worst fears. Buy the way all the advice you have receive is good advice, but I keep reading your inquiry.

First if you have had a trip why not just ohm it out and see if you have a fault with that?

Second take a real good look at your system how well has it been maintained, is everything well maintained? As long as you are down has all the equipment been cleaned and repaired? What else could cause the line to trip out? Personally, I would walk through a commissioning checklist and have the inspectors sign off before I reactivated a possible 69KV line.

Now to address you question. There are many companies who keep a Megger around as standard test equipment. So in order to avoid cost you might try to check the line with that. To my knowledge a Megger will not do any significant damage to a 69 KV power line or its equipment.

Hi pot testing is a different story. It is an expensive piece of equipment and you need certified testers to operate it and it is not something a lot of companies have laying around just because they may need it someday. If you decide to Hi pot the line, it will find any faults even if that is not what caused the original trip. You say in your question that this line has 3 splices in it already, the Hi pot will probably fail them.

So if you decided to Hi pot the cables I don't see need to run the Megger next.

Register to Reply Score 1 for Good Answer
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

andreY (1); Anonymous Poster (1); electricalexpert65 (1); GRAY HAIRED OLD GOAT (1); JohnDG (1); Saqi (1); U NO WHO (1)

Previous in Forum: Sizing Resistors for Reduced Voltage Primary Resistance   Next in Forum: current carring capacity of conductor
You might be interested in: Hipot Testers, Cable Laying Services, Cable Assemblies

Advertisement