Anonymous Poster

Sizing Resistors for Reduced Voltage Primary Resistance

01/13/2010 9:02 PM

I am an instructor for an inside electrical apprenticeship program, and I am teaching motor controls. We already have an entire room set up as a lab for motor controls that we built ourselves with a significant ammount of donated equipment. Therefore we have a variety of motors at the lab stations. I have looked for hours on the web for the mathematics and formulas used to size primary resistance starters (squirrelcage, not wound rotor) and have found nothing. I am not looking for someone to size them for me. I can handle the math and the theory, so I am simply looking for either a resource or the formulas used to do this. Can anyone help?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#1

Re: sizing resistors for reduced voltage primary resistance starting

01/13/2010 11:17 PM

Hello Guest,

  1. AC or DC?
  2. Types of motors (stepper, servo, etc.)?
  3. Sizes of motors?
  4. Types of motor controls (inverters, H-bridge, etc.)?

Need more info!!!

(if you had registered, an email would AUTOMATICALLY be sent to you, notifying you of this reply, along with a clickable link taking you right here)

Mike

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Reply
Anonymous Poster
#9
In reply to #1

Re: sizing resistors for reduced voltage primary resistance starting

01/18/2010 10:40 AM

In his post he stated squirrel cage and wound rotor. I believe these to be ac motors.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Sizing Resistors for Reduced Voltage Primary Resistance Starting

01/14/2010 8:23 AM

It is simple. You first decide what percentage voltage you want to apply to the motor during starting. Then calculate the balance voltage to be dropped in the resistor taking this as the IR Drop, the I being the starting current.

To put it simply, let me take a 400V, 100A rated current motor, the starting current being 600A. Now, to reduce the starting current, I like to reduce the voltage applied to the motor to be only 50% of the rated voltage. That is 200V to be dropped in the external resistance.

I x R = 200V; I = 600A; then, R = 200/600 = 0.3333 Ohms. And the wattage rating would be: 200 x 600 = 120kW.

Reply
Participant

Join Date: May 2010
Posts: 1
#11
In reply to #2

Re: Sizing Resistors for Reduced Voltage Primary Resistance Starting

05/30/2010 6:10 AM

Is a 400v three phase motor draws 90amps what would the voltage across the motor have to be if i want it to start at 30amps??

is it as simple as 400/3?

how would i get my resistor size?

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Sizing Resistors for Reduced Voltage Primary Resistance Starting

01/14/2010 8:35 AM

Bear in mind that, under some circumstances, a series resistance on a parallel-wound motor may be sufficient for to take a long time to come up to speed, or even to not start at all. In this case either of the circuit protective device(s) or the motor protective device must operate before the motor and its supply cables become a convection heater. This may be achieved by:

  • selecting the circuit protective device(s) correctly so as to protect the cabling, and
  • the motor protective device to the full load current rating of the motor.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Jan 2007
Location: UK S.Northants
Posts: 485
Good Answers: 19
#4

Re: Sizing Resistors for Reduced Voltage Primary Resistance Starting

01/14/2010 11:29 AM

This [resistance starting] method is used with slip ring motors where the rotor poles can be accessed byway of the slip rings. Using brushes, variable power resistors are connected in series with the poles. During start-up the resistance is large and then reduced to zero at full speed.

At start-up the resistance results in the stator's field strength being weakened less. As a result, the inrush current is reduced. Another important advantage is higher start-up torque. As well, the resistors generate a phase shift in the field resulting in the magnetic force acting on the rotor having a favorable angle[citation needed].

http://en.wikipedia.org/wiki/Induction_motor from Wikipedia (yes, I know) I had never heard of resistance starting, only having experience of much lower-power motors, but you state you are applying them to squirrel cage and not wound rotor. Is there some confusion here?

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: Sizing Resistors for Reduced Voltage Primary Resistance Starting

01/14/2010 3:47 PM

I don't believe he is referring to a Wound Rotor Induction Motor, but rather a Primary Resistor starting method for a standard Squirrel Cage Induction Motor. It used to be a common method before the advent of Solid State starters, hardly anyone uses them any longer.

About the only place I still see them used is in older Crane Controls and Fire Pump controllers. You can start here for resources on how to select and size them.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Active Contributor

Join Date: Mar 2008
Location: Granite City, IL
Posts: 12
#6

Re: Sizing Resistors for Reduced Voltage Primary Resistance

01/15/2010 9:02 AM

The use of "ballast resistors" is considered old technology although we still see them being used in overhead cranes for the trolley & bridge motions. Little by little, they are being replaced with solid-state soft-starts. Power Electronics (www.peinfo.com) & Benshaw (http://benshaw.cwfc.com/) make excellent products.

Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#7

Re: Sizing Resistors for Reduced Voltage Primary Resistance

01/16/2010 5:26 AM

As an instructor,why not apply commom starting methods(DOL,STAR-DELTA) which still exist in most industries today,why u later take time to get your resistance starting formular,or even auto transformer starting methods?

There are no direct formular as far as i know.Just apply your usual ohms law and do some good calculations with the datas on the motors,just as electricalexpert is doing,then u may get your result.

Patrick Whowha

__________________
Patrick Whowha
Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#8

Re: Sizing Resistors for Reduced Voltage Primary Resistance

01/16/2010 7:26 AM

What u need is stator starters which comprise of (a)active resistors (b)star point starter (c) with chokes.

Taking active resistors for example,u will need to connect the resistors in series with the asynchronous motor in your lab.Note here that the starting voltage of the stator winding will reduce in direct proportion to starting current.

On the data plate of the motor,record the voltage(V) rating and current(I) rating.Take for example V=400V, I=5A. Motor could be say 2.2kw power rating, R=Resistance.

Apply V=IR, R=V/I =400/5 =80Ω. U will have to connect 80Ω x 3 Resistors in series with the motor if its a three phase motor with appropriate power rating of the motor so as not to burn the resistors.

Either use a contactor or manual 3pole switch for the line supply to motor and also for the three resistors to the motor.

Switch ON the resistors first in circuit,then switch ON supply through the Line contactor or manual switch,to reduce high starting current,then next,switch OFF the resistors through the contactor or manual switch connected across the resistors,leaving the motor to run with only the line contactor or manual switch and the line protection fuses or breakers.

U may connect ammeters on the lines to check the current or use clamp-on ammeter to check the current and your students will appreciate how motors could be started or controlled.Note,if u are connecting motor in star,use a star-point starter.The resistors in this case are connected to the W2,U2,V2 of the motor and having their ends bridged(STAR),while supply is fed to the U1,V1 and W1.

Note that using starters with active resistors have a drawback of causing energy losses.With chokes losses are lower,but power factor cosφ is poorer.With Stator starters,starting TORQUE is greatly reduced along with starting current.

Patrick Whowha

__________________
Patrick Whowha
Reply
Anonymous Poster
#10

Re: Sizing Resistors for Reduced Voltage Primary Resistance

01/18/2010 11:28 AM

Good for you. We need to be teaching this. Many of these systems are still in use and we need our wireman to be able to service them. Still one of the smoothest starting methods available, hence there use in cranes. We probably don't need to know how to engineer them, just repair them and therefore understand how they work. This website has some good info: http://www.scribd.com/doc/17252612/Motor-Starter