Commercial Range-Oven Change-out.

01/14/2010 9:53 AM

1. How do you measure the airflow in a MUA or Exhaust duct? The existing range-oven requires 800 cfm MakeUp Air and Exhaust Air. Is there a device that one can place by the MUA outlet register, and the Type I Hood exhaust inlet filter to measure the velocity, and then convert this value to a flow rate, using the area of the duct or filter (Q = V * A) ? The new unit requires 1000 cfm.

2. The existing centrifugal upblast direct drive exhaust fan with 1/2 hp motor currently provides an 800 cfm flow rate at 1314 rpm. The manufacturer has stated it can be field-adjusted to provide 1200 cfm at 1500 rpm. I have interpolated to arrive at a 1000 cfm flow rate at 1407 rpm. I think it has a rheostat-type dial to vary the output.

3. The MakeUp Air is a dedicated evaporative cooler. I am told it can be wired for low, medium, or high output, to the maximum capacity of 3200 cfm. How can one determine the flow rates coincident with the settings?

4. The existing MUA outlet register has been installed inside the hood, a few inches in front of the Exhaust inlet filters. Is this common?

5. The Code requires the Exhaust duct flow velocity shall be at least 500 ft/min (IMC 506.3.4). The existing 9" square duct velocity at 800 cfm is 1420 ft/min. The new 1000 cfm flow rate in the same duct will result in a velocity of 1778 ft/min. I could find no maximum flow velocity. Is there a rule of thumb for max exhaust velocity?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Commercial Range-Oven Change-out.

01/14/2010 11:40 AM

An anemometer will measure air flow.

Register to Reply
Power-User
United States - Member - Engineering Fields - Mechanical Engineering - Hobbies - Fishing - Hobbies - Musician -

Join Date: Jun 2009
Location: California
Posts: 106
Good Answers: 19
#2

Re: Commercial Range-Oven Change-out.

01/14/2010 5:32 PM

1 - As previously mentioned, a vane or hot-wire anemometer can be used to get velocity readings in the duct, from which volume can be determined (VxA). You will need a small hole in the duct to insert the anemometer and should take several traverse readings to get an good average velocity. Anemometers can range widely in price & quality - check omega.com for a decent, low-cost one. Air balancers also use a flow hood that fits over a supply grille (usually 2'x2') and provides velocity readings, although they are fairly expensive.

2 - Per fan affinity laws, Q1/Q2 = n1/n2 and the differential pressure dp1/dp2 = (n1/n2)2. The increase in volume (50%) for such a small increase in speed (14%) seems incorrect - perhaps they have reported this performance at the same dp as for operation at 1314 rpm, but the dp will actually be higher due to higher air velocity. The actual flow should be pretty close to that predicited by affinity laws, (1500/1314) x 800 = 913 cfm. Ask the mfr for fan curves at each speed and overlay with your system curve to find out what you can really get out of the fan.

3 - Get the mfr & model off the nameplate and get an IOM manual from the mfr.

4 - This is not the way I would design it, but I don't think there is a code issue with it. If the MUA register is properly adjusted, the throw should prevent short circuiting, but it also might blow some of the fumes/smoke into the space.

5 - Higher velocity = higher friction/pressure loss, resulting in more power required. Per affinity laws, P1/P2 = (n1/n2)3 so even small increases in speed can result in large increases in power requirements. Given the size and velocity you posted, the pressure drop is about 1.5" WC/100 ft of duct (get a Ductulator or similar from HVAC mfr) which is alot higher than I would size at, but is probably OK as long as you dont overload the fan motor (confirm with fan curves). The other issue that you may run into by increasing velocity is that it will get noisier, which might cause complaints depending on current noise levels.

Register to Reply
Power-User
United States - Member - New Member

Join Date: May 2008
Location: Arizona
Posts: 355
Good Answers: 4
#4
In reply to #2

Re: Commercial Range-Oven Change-out.

01/19/2010 1:09 PM

Good morning dac1267, 1. Thx for the lead to the anemometers. I have requested the flow quantities on the existing ducts.

2. Based on the affinity laws, I have calculated the new 1000 cfm flow rate based on 1642 rpm. However, in looking at the Performance Table for the installed fan, for 0.375"wc ESP and 1350 rpm, the flow rate would be 1546 cfm. I estimate the friction loss at 0.33"wc based on your 1.5"wc/100'. So, based on the Table, the flow rate may already be at or over the required 1000 cfm.

Surprisingly, at 800 cfm and 0.33"wc ESP, the required rpm falls far below the minimum fan speed of 1150 rpm. At the new flow rate of 1000 cfm and an estimated new ESP of 0.5"wc, the new required rpm is still below the minimum rpm.

3. The contractor is to supply more detailed manufacturer data on the MUA unit.

4. MUA Discharge Grille location inside hood. The contractor chose that location based on a recommendation by the exhaust duct fabricator, who does this type of work in the area. The City Fire Inspector did not like this location, but approved it anyway.

5. Based on an existing equivalent exhaust duct length of 22', I estimate the friction loss at 0.33"wc.

Thx to you and the others who offered opinions.

Register to Reply
Commentator

Join Date: May 2009
Posts: 64
Good Answers: 6
#3

Re: Commercial Range-Oven Change-out.

01/15/2010 12:14 AM

Its been a while, however, I believe that the code you need to apply for the exhaust duct is NFPA-96, for commercial exhaust from a range hood. Depending on the local building code, you will need to verify which version (meaning year as it changes frequently) they require you use. The minimum exhaust velocity will be given there, although from memory I believe it is 1500 fpm. You will have to confirm with local authorities.

You may need to revise the duct to meet the code as well depending on when it was built. Also, there may be other issues. These things can turn out to be much larger than initially anticipated. You will have to do your homework on this one, because these issues tend to be up to the AHJ.

Cheers,

Duane