Energy Meter

01/14/2010 11:46 AM

I have an electromagnetic energy meter with following details:

PT - 3*11000/110V, CT - 500/5A, Kh - 0.25 rev/ kWh, double element, 6 digit register.

The multiplication factor should have been 10000. However, the meter facia indicates a MF of 100. I understand that the factor 10000 derived from PT, CT ratio has been multiplied by a factor 0.01. What is this factor and how can I find out that value.

Also, the meter manufacturer is VALMET and the meter type is KJ5. Can anyone provide me with the details regarding this energy meter. The meter was installed in the year 1985.

Register to Reply
Pathfinder Tags: Energy Meter
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Energy Meter

01/14/2010 5:30 PM

The multiplication factor is the PT Ratio X The CT ratio. From the nameplate the

PT ratio is 11000/110 = 100 CT ratio is 500/5 = 100 100 x 100 = 10000. If the MF has been change to 100, you have a change in the PT or CT ratios. You may not have a PT installed and thus the MF = 100

Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Energy Meter

01/14/2010 5:49 PM

First of all I would request you to go to the previous posting and read the comment # 4: http://cr4.globalspec.com/thread/36700/M-F-in-Electricity-bill

It is not necessarily true that the energy meter multiplication factor (M.F) is the multiplication of the CT ratio and PT ratio (there may be a M.F for a meter which doesn't even use CT or PT at all). If you use PT of 3*11000/110V and CT of 500/5A for this meter, the M.F is the value written on the meter front dial. Your meter is designed for this PT and CT ratio with a multiplication factor 100. However, if you use the PT and CT of different ratio other than the mentioned ones, then you have to calculate the M.F as mentioned in case 4 (of comment # 4) for the above posting.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Dec 2009
Location: Mangalore, India
Posts: 65
Good Answers: 4
#6
In reply to #2

Re: Energy Meter

01/15/2010 8:05 AM

Thanks for the reply. But how do we derive the multiplication factor of an energy meter which doesn't use CT and/or PT. Is this some kind of gear ratio inside the energy meter.

Register to Reply
Commentator

Join Date: Dec 2009
Location: Mangalore, India
Posts: 65
Good Answers: 4
#5
In reply to #1

Re: Energy Meter

01/15/2010 7:59 AM

There is a PT installed and the system has remained untouched for the past 25 years. The PT is 11000/110V and CT 500/5A.

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#3

Re: Energy Meter

01/14/2010 10:31 PM

The multiplication factor depends on 3 variables: PT ratio, CT ratio and Kh. Kh is the number of KWh per rotation of the meter disk. Even though solid-state meters do not actually have an induction disk, the Kh value is still used. In your case, Kh = 0.25.

Therefore, the multiplication factor is:

PTR x CTR x Kh = 100 x 100 x 0.25 = 2500

In electronic meters, there is an additional factor. The display can be programmed to better suit the load. For example, the calculation above indicates that the meter register will only change when 2.5 MWh of energy has been consumed. That's not very precise when most places charge by the KWh.

It is also possible that the service has been modified in the last 25 years, and the PTR and/or CTR is different now.

To determine the actual multiplier for the display, connect a constant resistance load to the meter. Measure the voltage and current at the meter inputs. Wait until the display ticks over, then time how long it takes to tick over again. The actual usage will be:

KWh = (Volts x Amperes (x √3 for 3 phase) x PTR x CTR) x time in seconds / 3600

Divide the actual usage by the display. That value will be the actual meter multiplier.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply Score 1 for Good Answer
Anonymous Poster
#4
In reply to #3

Re: Energy Meter

01/14/2010 10:57 PM

Now, 3 M.F values 10000, 2500 and 100. Which one is correct?

I worked with electrical commercial and used lot of energy meter. With my experience,the meter dial M.F value 100 is correct.

Register to Reply
Member

Join Date: Oct 2009
Posts: 5
#7
In reply to #4

Re: Energy Meter

01/16/2010 6:55 AM

The 100 MF of the company should be correct, since as per the calculation for the MF it is CTRatio x PTRatio, which works out to be 10000 in the present case, the manufacturer by using some gear trains for the cyclometer for the energy meter must have used the MF 100.

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#8
In reply to #4

Re: Energy Meter

01/28/2010 10:02 AM

Guest,

All of the multipliers in my previous post must be used for the meter to provide accurate energy data. In most cases, the meter dial assumes direct connection, meaning no instrument transformers (PT's or CT's) are involved. In that case, the PTR and the CTR both equal 1.0, and can be ignored.

In cases where the voltage or current is too high for direct connection (for example, a 3300V, 2,000A industrial service, potential and current transformers must be used between the line and the meter. The transformation ratios of these transformers must be included in the calculation.

FYI, I have worked in the electric utility field for over 30 years, as an electrician, instrument technician and engineer, and have designed, installed and commissioned literally thousands of metering systems on everything from 240V, 200A residential services to 138,000V, 3,000A utility grid interconnections.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Active Contributor

Join Date: Nov 2011
Posts: 12
#9

Re: Energy Meter

02/13/2012 4:02 AM

hi there

some of electical energy meters has mechanical intenal MF ( 100/5 )

the result of elec. MF must multiplide to inverce mechanical one.

in this case if there is mech MF :

1-elec MF = (11000/110)X(500/5)=10000.

2-mech internal MF = 100/5=20 inverse = 5/100.

main Mf = 10000/200=10000x5/100=500.

I thaught that

Thanks

__________________
sokrer
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Electronaut (2); msamad (1); puppalank (1); pwr2thepeople (2); sokrer (1); wareagle (1)

Previous in Forum: Hyster E20 Error Code   Next in Forum: How Do Linear Actuators Work?

Advertisement