Electrical Design Specifications

01/15/2010 1:16 PM

Greetings all,

iam working in an out door lighting design for our plant and i calculated the total watt needed (sum of all lights) = 53 kw, 220 volt

our power supply is 480V

so, I chosed a 75 KVA transformer dry type 480/220-127 V 3 phase 60 Hz

cable size from feeder to transformer primary = 50 mm2 (1/0 AWG)

cable size from transformer secondary to distribution panel board = 125 mm2 (250 MCM)

distribution panel board main breacker = 250 A

So, are my calculations ok ? any changes or suggestions ?

thanks in advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#1

Re: Electrical Design Specifications

01/16/2010 4:58 AM

How did u arrive at 75kva transformer? How did u get your power factor pf,how did u get your total load current? wt calculation using 480v or 220v?What criteria did u use to select your cable size of 50mm and 125mm for a 53kw total load?

If u are not very sure of your calculated values,consult a professional to do it for u or else provide a detailed information.

Patrick Whowha

__________________
Patrick Whowha
Register to Reply
Participant

Join Date: Jan 2010
Posts: 2
#2
In reply to #1

Re: Electrical Design Specifications

01/16/2010 8:50 AM

- power factor pf= 0.8, P(W)=IV * PF, the light source HPMV = 400 W, V=220 V, I=2.3 A

- transformer size => 75 KVA* PF = 60 KW, 7KW higher than needed KW

- calculation using 220 V

-cable size according to transformer max. capacity = 75 KVA, I= KVA/V, V= 480 Pri. & 220 Sec. => I= 156 A (Pri), 340 A (Sec)

load = 53 KW, but we may add loads in the future so I chosed cable size for maximum use.

- Iam sure about my calculations, but these are all using formulas and theory, I just wnna make sure that i did not miss anything.

reagards

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Electrical Design Specifications

01/16/2010 6:06 PM

(75,000 VA ÷ 480) ÷ √3 ≈ 90.2 A.

For conductors, 90.2 x 1.25 ≈ 113 A.

For this size of transformer primary CB is also (if memory serves) 90.2 x 1.25; the next standard size is 125 A.

And calculate similarly for the secondary. It looks as though the 1/√3 factor was missing from the original 3-phase calculations.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster
#4
In reply to #3

Re: Electrical Design Specifications

01/16/2010 11:28 PM

thanks a lot, i missed that one

Register to Reply
Associate

Join Date: Nov 2007
Posts: 50
#5

Re: Electrical Design Specifications

01/18/2010 10:00 AM

I wouldn't rely on the cable rating alone (max amps). The more thorough method would be to make in-depth voltage drop calculations. Your posting indicates that all loads will be on a single circuit. Multiple circuits (multiple contactors and CBs) would lower the load on each cable, reducing min. cable sizes, thus reducing costs.