Earth fault & restricted earth fault

01/17/2010 11:44 AM

What is the difference between earth fault & restricted earth fault?
Please explain.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Earth fault & restricted earth fault

01/17/2010 8:14 PM
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Earth fault & restricted earth fault

01/18/2010 9:00 AM

(Plain) Earth fault protection scheme would respond for any earth fault current beyond the setting, irrespective of the location of the fault in the network. Whereas, restricted earth fault protection scheme, as the name suggests, would respond only to those earth faults, which are happening in a pre-defined zone of protection. If the earth fault is outside this zone, even if the fault curent is more than the setting, the scheme wouldn't respond.