Vector group changing

01/19/2010 12:32 PM

An internally connected Dyn11 transformer can be changed to either Dyn3 , Dyn5 , Dyn7 , Dyn9 or Dyn11 transformer , by doing external changes on both sides of the transformer . Verify the above mentioned statement....

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#1

Re: Vector group changing

01/22/2010 4:54 AM

Dear all,

Dyn11 transformer can be converted to Dyn 3 ad Dyn7 by changing the secondary terminal marking. So, your statement is correct for Dyn 3 and Dyn 7.

For Dyn 1, Dyn 9, Dyn 5 secondary neutral must be re-wired, thus only external chage is not enough for these.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply