BTG Consistency Meters

01/20/2010 10:42 AM

hey people, anyone here have any experince with BTG consistecy meters? I have one here in a pulp paper mill, and everytime we shutdown for a while and start back up the reading changes, only once in a while though. Any suggestions?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#1

Re: BTG Consistency Meters

01/20/2010 11:54 AM

One possibility is that you have a valve that is not shutting properly. That will cause the pulp stock in the line to de-water, and give a higher reading upon startup.

If you have a data historian, try to correlate the amount of downtime with the reading change. I.E. A 2 hour shutdown causes no significant change, but after an 8 hour shutdown a significant change is recorded.

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Reply