what disadvantages to use same core for over cuurent and differential protection

01/24/2010 1:40 AM

what is the disadvantages to use the same core of a CT in differential and over current protection of a transformer 132/ 33 and 25 mva

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Participant
India - Member - New Member

Join Date: Aug 2007
Posts: 4
#1

Re: what disadvantages to use same core for over cuurent and differential protection

01/24/2010 6:47 AM

Accuracy class and saturation level of both the core are diffrent.

Reply
Active Contributor

Join Date: Dec 2009
Posts: 14
#2

Re: what disadvantages to use same core for over cuurent and differential protection

01/25/2010 12:02 AM

Due to difference in % composit errors, during through fault condition unwanted trip may occur.

rajuS

Reply
Member

Join Date: Dec 2008
Posts: 6
#3

Re: what disadvantages to use same core for over cuurent and differential protection

01/25/2010 12:50 AM

Usually back up protection should use separate core as it can operate independant of main protection components to take care of failure of main protection CT, shorting of its secondary wiring. Technically, if burden is within limits, you can use same core for differential and over current protection.

Reply Score 1 for Good Answer
Active Contributor

Join Date: Jul 2008
Posts: 15
#4

Re: what disadvantages to use same core for over cuurent and differential protection

01/25/2010 3:02 AM

you can actually do that from pratical experience by applying principle of convertion through solid state.with addition of few component through ac-ac or dc-dc depending on the type of protection you are looking.but mind you the design should witstand high voltage relative to your source of supply and load matching and efc.

Reply Off Topic (Score 5)
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Iruero.o. James (1); musef_111 (1); raju11 (1); rajukailas (1)